    Unhappy Never ending cleaning condensor



    Hi Guys,
    I have 2 screw compressors (at a cruising ship) and big problems with dirty condensor. Due to all mud it's need to clean it in mechanicel way often specielly in summer time. Now I heard that there is some kind of small round plastic balls to use (with re-cycling) do anyone heard about this or has anyone some tips how to solve this problem?

    Drefer



  2. #2
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Never ending cleaning condensor

    Hi

    I have used this http://www.kamco.co.uk/FX.htm on the few occasions where I have been lucky enough to stuble upon a condencer fittet with recirculation

    It's called Descalex or descaling liquid.
    -Cheers-

    Tycho

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Never ending cleaning condensor

    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Aug 2001
    Location
    NE Lincolnshire, UK
    Posts
    145
    Rep Power
    23

    Re: Never ending cleaning condensor

    Quote Originally Posted by Drefer
    Hi Guys,
    Due to all mud it's need to clean it in mechanicel way often specielly in summer time.
    I am assuming it is water drawn in from the surrounding sea that acts as the coolant.

    If you clean it, what stops the mud getting in again, and why? Seems that the water intakes should be positioned so as not to pick up mud, and would have some kind of filtration system.

    The other thought is water flow. Have you had any problems with water flow restriction that may cause the mud to settle out instead of getting flushed through the tubes by a strong flow? Again, intake filter blocked?

    Steve

  5. #5
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Never ending cleaning condensor

    Hi Drefer

    what about the Total Desolved Solids, if the condenser doesnot bleed off a small amount of the sump water the TDS will build up causing a slurry in the sump

    Kind Regards, Andy

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Never ending cleaning condensor

    That's in case of a tube in tube condensor I suppose.
    Problem with these is that the end covers must be specially be threated (coated) for the seawater.

    You better use for this application plate HE, compact, cheaper and reliable.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Never ending cleaning condensor

    In case of a tube in tube the inside of the tubes is the water side, so can yoi then have TSD?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Never ending cleaning condenser

    If you are using seawater the dirt problem probably develops when you are in port.

    Several things I can recommend to you for investigation:

    The water velocity may be too low to provide a cleaning action on the tubes. If the condenser has enhanced surface tubes on the inside surface they will look like a rifle barrel with grooves. The grooves can accumulate material more quickly than a prime surface tube (smooth inside).

    The brushes Peter is describing should work OK for that purpose.

    Another consideration is to use a centrifugal separator to remove as much dirt as possible from the water before the water flows into the condenser. You may have to use a basket filter downstream of the separator to catch the small particles.

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Never ending cleaning condenser

    It's not always because they lay in the harbor.

    The temperature in the condenser is mostly at ideal warm conditions to let grow bacteria to some sort of slime inside the tubes.

    In my begin days when I learned the job, we worked many times on very bigs container boats.

    Placing a mesh filter in an open system is a must and I think this is done.With bypass valves over the filter so that it can be cleaned/removed very quickly and easily

    Even with a closed system with a chiller, we always install a filter to remove debris while installing the system.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Aug 2005
    Location
    england
    Posts
    7
    Rep Power
    0

    Red face Re: Never ending cleaning condensor

    Reminds me of my Navy days.
    I agree with some of the comments below, first check is filtration on your inlet, should be duplex filters fitted. If there is a recirculation system fitted ensure this is allowing as much water to bleed off as possible (I would think though that it was a single pass penn valve type though, check velocity is high enough and check pump flow rate.
    Always an issue in ports though if you are out a lot you should not get a lot of problems apart from if in high temperature waters with low velocities.....

  11. #11
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Never ending cleaning condensor

    Quote Originally Posted by Peter_1
    It's not always because they lay in the harbor.

    The temperature in the condenser is mostly at ideal warm conditions to let grow bacteria to some sort of slime inside the tubes.
    I agree with you Peter. There are a lot of possible factors to consider. Drefer mentioned mud in his post and it was my thought that this could be caused by the water conditions created by the ship in port.

Similar Threads

  1. pipe freezing just outside the compressor
    By guestingmale in forum Domestic
    Replies: 71
    Last Post: 24-08-2008, 07:57 PM
  2. Airflow through condensor
    By Peter_1 in forum Air Conditioning
    Replies: 1
    Last Post: 29-10-2005, 10:31 PM
  3. Condensor Fans Control
    By Feeze in forum Commissioning
    Replies: 37
    Last Post: 18-10-2004, 10:00 PM
  4. Condensor selection
    By bersaga in forum Industrial
    Replies: 4
    Last Post: 23-01-2003, 01:17 AM
  5. Condenser question
    By Steve25 in forum Technical Speculations
    Replies: 16
    Last Post: 08-01-2003, 09:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •