    Daikin VRV11 Unit 0 H4 fault code HELP



    Installing REYQ16M81B With FXFQ- ( 5,6.3,8)- M7V1B total of 5 cassettes with 5 BS100 boxes
    Second-hand unit fitted in charity office history not known came with 10 bs boxex and cassettes
    All indoor units are on same phase and out door L1L2L3 is clock wise
    It came on with one cassette not working bs f2 cable was out after connecting unit showing H4 and
    H2P FLASHING H3P ON
    Can any body help and Is there any way to reset the unit to factory



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    did you drive the levs open via the outdoor unit-
    vrv2 req the wiring test to be performed

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    https://drive.google.com/file/d/0Bz6...ew?usp=sharing
    click on link for vrv2 service manual

  4. #4
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    sorry myfirst daikin and it is vrv
    the manule i got from daikin saye u4 no power to out / in door unit inc phase interruption
    the the one u send 2.43 “U4” Malfunction of Transmission Between Indoor Units ......................222

    which do i go for?

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    u4 comms error between indoor - outdoor or indoor -bs unit- you mentioned
    but im sure if you powered it up 1st time you need to perform the wiring check to remedy this
    first power it all down power up the indoors ,bc boxes and then the outdoor
    go in setting mode 1 and select operation via ind- led should be a solid yellow light
    prey that whe it was decomissioned that the valves were driven open for degassing and you pressure tested,vacced and charged prior to powering up

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    you can check at the outdoor how many bc boxes and how many indoors it can see

  7. #7
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    dont know decommissioning but it was pressure tested vaced for 24 hours and charged to factory charge

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    have you measured the piperun, on the back panel of the condenser there should be a chart for calculating the additional charge- based on length of run

  9. #9
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    haw do i check that i a sad my first vrv sorry i have not a clue

  10. #10
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    10 m to bs 4m bs to cassette

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin VRV11 Unit 0 H4 fault code HELP


  12. #12
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    the total run
    outdoor to 1st bs bs to 1st cass bc1 to bc 2 bc2 to 2nd cass bc2-bc3 bc3 to cass
    also pipesizes are needed as you need the toatl length of liquid line for example in 1/2,3/8.1/4 total suction line 1 3/8 if any , 1 1/8 , 7/8,3/4
    did you get daikin to do the pipe size calc as after the 2nd refnet youll prob drop down a pipe size, also all refnets horizontal, and pipework musnt be clamped too tight, hydrazorbs are a no no they recommend running pipe on tray and securing with cable ties
    Quote Originally Posted by cryotec View Post
    10 m to bs 4m bs to cassette

  13. #13
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    10m each 1 1/8, 7/8, 1/2
    12m each 1/4, 1/2
    8m each 3/8., 5/8

  14. #14
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    wiring as u sad outside to bs 1 to 2,3,4,5
    bs1 to cassette 1 2to 2 and so on

    two controllers one p1 p2 of cassette 1,2,3
    2nd to 4,5
    Last edited by cryotec; 20-12-2014 at 11:46 PM.

  15. #15
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin VRV11 Unit 0 H4 fault code HELP


  16. #16
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    could be worse- my first vrv install was in belfast a 2 pipe on 7 cassettes and a 3 pipe on 5 cassettes, sparkie wired radial supplies to each indoor from the basement- must have used about 3 miles of cable- told him to ring each floor, didnt have daikin produce pipe sizing layout drawing, condensers on 5th fl roof , had leaks in the riser as my brazing wasnt the best, did it with an apprentice, and did it in 11 days, but did 230 hrs - you never forget your 1st vrv install,read the manuals and mither daikin technical - think vrv2 has auto charge function on it so you should be ok

  17. #17
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    3 pipe to bs 1 1/8, 7/8, 1/2
    5 cassette 2 pipe from bs

    is there any way to reset to factory setting as i don't know what has been changed

  18. #18
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    PressPress and hold the Reset button on the outdoor PCB for more than 5 seconds forces the system to re_handshake connected indoor units/bs boxes

  19. #19
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    not that one master reset so it is factory default

  20. #20
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    PressPress and hold the Mode button for 10 seconds. You will need to carry out the Test function after this to clear the UC error
    Last edited by frank; 23-12-2014 at 01:04 PM.

  21. #21
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Daikin VRV11 Unit 0 H4 fault code HELP

    Thanks boys it all sorted ----