Results 1 to 6 of 6
  1. #1
    Join Date
    Apr 2006
    Location
    Iraq
    Posts
    5
    Rep Power
    0

    Expantion valve adjustment



    If the TXV are not correctly setting,How can i Know that ?,and what will i need tools to get adjust it?and how?

    Thanx



  2. #2
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,058
    Rep Power
    24

    Re: Expantion valve adjustment

    You need to be methodical. You can't rush this job. It is not difficult. In practical terms at the job site you will need:

    1. Hand tools.
    2. An accurate surface thermometer
    3. An accurate pressure gauge,
    4. Pressure / temperature charts for the refrigerant you are using.
    5. Note book and pen
    6. Patience, because you may need to observe the working of the unit for some time.


    The TXV controls the superheat at the exit of the evaporator. So, you will need to know what the design superheat is. Typically it will be about 5 degrees C, but it can vary from job to job.


    1. Check you have the correct valve, it has the correct sensing element for the refrigerant you are using and is fitted with the correct size of orifice. Check all this first before you do anything else.

    2. If you have a pressure sensing tapping at the evaporator end or can install one, attach your pressure gauge here. This is the best place. If not, work out the pressure loss in the suction pipe and put your gauge on the service port at the compressor. You will have to factor the pressure loss every time you make a reading and it is less accurate.

    3. If the TXV has an equalising line, you should not need to worry about the internal pressure loss in the evaporator. If it has, make sure that it and the sensing bulb are installed in line with the manufacturer?s instructions.

    4. Fix your thermometer sensor near the TXV bulb, best to use a thermal contact paste and insulate it.

    5. Start the unit and allow it to stabilise ? about 20 minutes. Ensure that it has the correct refrigerant charge.

    6. Compare the temperature reading at the TXV bulb with the saturation temperature at your pressure reading (adjusted for line loss if necessary.

    7. Do nothing for at least half an hour. Compare the readings at 5 minute intervals.

    8. If they are stable, do not vary much and at the superheat values you want, do nothing.

    9. If you need to adjust the TXV, follow the manufacturer?s instructions, turn the spindle only half a turn each time and write it in your book. Allow 10 minutes between each adjustment and record the results until you get a stable superheat at the desired value.


    .
    ________
    Mazda Sentia specifications
    Last edited by Argus; 07-02-2011 at 10:04 AM.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Expantion valve adjustment

    Hi ayaz,

    Welcome to the RE forum.

    The tools required are a simple set of hand tools; Adjustable wrenches or spanners, whatever term you prefer to use.

    If the valve has been correctly selected for the operating conditions, the valve may occasionally require a one time adjustment.

    These valves do not require regular adjustment for them to work properly.

    Below is a link to a bulletin that provides some additional information on valve operation, selection, and adjustment.

    http://www.sporlan.com/10-9.pdf

    The valve controls the superheat from the evaporator. The bulletin will show you how to adjust this.

    I hope this is helpful.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Expantion valve adjustment

    The most important tool : your brain and the knowledge to understand what you're doing.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Apr 2006
    Location
    UK
    Posts
    77
    Rep Power
    19

    Re: Expantion valve adjustment

    You are probably adjusting an old system as if you were sent for comisioning ,you would already know what tools.In which case it should already have been done.If the system is frosting back check the bulb is not loose.Make sure the bulb is insulated.Make sure the evap is not iced up.Is the system over charged?Has the system had a leaks and has lost vapour only on a refrigerant blend?Is the evap starved?If so is the system fully charged?dryer blocked?TEV filter blocked?.If none of the above change the Valve it's probably nacked.

  6. #6
    Join Date
    Apr 2006
    Location
    Iraq
    Posts
    5
    Rep Power
    0

    Re: Expantion valve adjustment

    I want to thank every one replied in this subject,all information were very helpfull.

    thanx for all

    Ayaz

Similar Threads

  1. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  2. Scotsman commercial H2O inlet valve
    By fullcourt in forum Trouble Shooting
    Replies: 9
    Last Post: 25-04-2006, 11:41 PM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 01:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •