Results 1 to 5 of 5
  1. #1
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Single Phase inverter condensing unit



    I want to built-up a chilled water cooling system with a single phase inverter condensing unit. The temperature of the cooling water will be maintaining at around 8 degrees C. But how am I going to produce a signal to the condensing unit to call for the inverter condensing unit to start and also to control the temperature of the chilled water. Is it possible to start an inverter condensing unit without using the indoor pcb circuit and controls, how am I able to control the temperature, please advice, thank you for your feedback.



  2. #2
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Single Phase inverter condensing unit

    Hi Cofreth
    The signal to start the invertor and control the speed of the compressor depends on the Invertor type. Most Invertors use either a 0-10volt signal or a 0/4-20ma signal. So you require a sensor that can give you one of these signals from a sensor measuring the chilled water flow or return temperature. You then set in the invertor the temperature you require the invertor to control at, and then calibrate the input signal accordingly. Most Invertor manufacturers also supply various control devices to match their invertor, but I know that Danfoss in their industrial sensors can supply suitable temperature sensors with 4-20ma out put.
    Once you have calibrated the sensor to the invertor you simply give the invertor a GO signal interlocked with a flow switch, and the invertor will speed up and down with the signal coming from the sensor. The invertor will have many options of how it operates but you need to discus this with the invertor supplier who should be able to help you set the Invertor parameters to satisfy the application Good Luck your going the right way

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Single Phase inverter condensing unit

    Are you planning to modify a air con system, or is this a proper refrigeration condensing unit?

    If its air con, you are going to have to fool it into thinking it is still cooling air and connected to its proper indoor unit.
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Single Phase inverter condensing unit

    best option is use a fridge condensing unit 3phase compressor and fitting an abb ach550 inverter drive or other similar then you can customise the ramp up time- either based on just time or as glen mentions using a transducer giving a variable output- using an inverter ac condenser wont work as you would need an indoor pcb to communicate with the outdoor and the sensors for coil temp,return air woudnt work in your application

  5. #5
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: Single Phase inverter condensing unit

    Quote Originally Posted by monkey spanners View Post
    Are you planning to modify a air con system, or is this a proper refrigeration condensing unit?

    If its air con, you are going to have to fool it into thinking it is still cooling air and connected to its proper indoor unit.
    Hi monkey spanners,

    Yes, I plan to use a normal air-con inverter condensing unit as the present market here, nobody is selling non inverter air-conditioner anymore.

    So in your opinion, I have to use back all indoor pcb, sensors , indoor fan motor and swing motor etc to fool the system to start-up, how about the control of water temperature, as the wireless remote controller can only set to lowest 15 degrees C.

    I wonder a 5-10V or 4-20ma can startup the air-con inverter condensing unit thru the signal input n the condensing unit, thanks.