    Hi frens..
    on Sanyo VRF of ODU.SPW-C1405DXHN8, i am getting error L18
    on remote.according to the error code it says 4 way valve operation
    failure, but i have checked it, and it seems OK.on heating mode
    when i on the units, up to 5 minutes it works perfectly and after
    5 minutes error occurs again after few minutes it works, after
    5 minutes it repeats the error.i have combine three units into one
    with same model number.so please guide me how to solve this
    problem.waiting for your warm answer..



  2. #2
    Join Date
    Nov 2008
    Location
    nepal
    Posts
    125
    Rep Power
    16

    Re: Sanyo VRF Error L18

    hi frens..
    any help for above problem...?

  3. #3
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Sanyo VRF Error L18

    During heating operation (Comp. ON), the highest detected temperature at an outdoor unit
    heat exchanger (EXG 1, EXG 2, EXL 1, or EXL 2) was 20°C or more above the outdoor air
    temperature (Air Temp.) continuously for 5 minutes or longer, or the detected suction
    temperature (SCT) was 20°C or more above the outdoor air temperature continuously for
    5 minutes or longer.

    Check sensors.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Sanyo VRF Error L18

    L18
    4-way valve operation failure
    During heating operation (Comp. ON), the highest detected temperature at an outdoor unit
    heat exchanger (EXG 1, EXG 2, EXL 1, or EXL 2) was 20°C or more above the outdoor air
    temperature (Air Temp.) continuously for 5 minutes or longer, or the detected suction
    temperature (SCT) was 20°C or more above the outdoor air temperature continuously for
    5 minutes or longer.
    (1) The 4-way valve connector (20S CN022) has become disconnected from the control PCB.
    (1) Check the 4-way valve connector (20S CN022).
    If the connector is normal, correct or replace the problem locations
    summary is a bit vague

  5. #5
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Sanyo VRF Error L18

    Without checker for ECO hard to find that error, but you can see all parametrs from wired controller.

  6. #6
    Join Date
    Nov 2008
    Location
    nepal
    Posts
    125
    Rep Power
    16

    Re: Sanyo VRF Error L18

    Dear sir,
    i will check it as per your advice....
    @Rusbuka: which model number of wired remote controller i can see all the parameters?