    Aug 2001
    ireland
    Climaveneta chiller fault E003
    Going to see a chiller with E003 fault actually its supposed to be affecting 2 chillers so I am presuming something remote from the chiller like a flow problem. Any ideas. I will update tomorrow after looking at it.
    4,712
    Re: Climaveneta chiller fault E003
    Hi techni.
    You are spot on.
    E003 is chilled water flow switch.
    So logically your assumption is correct.
    Good luck Grizzly
    Aug 2001
    ireland
    yes Grizzly BMS problem pumps not running and anti freeze protection working. Funny thing I have to go back tomorrow and meet the BMS guy as I also discovered that since I was last there somebody has changed the setpoint to control on the return temp.
    4,712
    Hi Techni.
    Thanks for the update.
    You could be attending due to Low temp issues or freeze protection for a pastime!
    As I suspect you already know return water temp control leaves the chiller exposed.
    Useful; when operating with low loads but only if you are not to near your freeze protection values.
    Is the Sp. on the BMS then or the Controller?
    Which controller do you have?
    Cheers Grizzly
    Aug 2001
    ireland
    Grizzly, previously the setpoint was on the controller but somebody (BMS engineer) must have changed it. I had to set the chiller at 13 C before I left and the leaving temp was 7.5C, so i have to get back early in the morning to get things changed. Is there a way to change it on the controller? It's a CVM-2000 and duty is 1150kW approx.