    Delonghi r410a Air Source Heat Pump High Pressure problem



    Hi
    Looking for some technical assistance for a Delonghi Bran Air Source Heat Pump it's r410a.
    It's tripping the high pressure switch when it gets to high outlet temperatures on hot water.
    Measured 5 bar on low side and it is hitting the high side limit at 38 bar when water flow temperature is about 52oc.
    Temperature at expansion valve seemed constant around -6oc.
    Plenty of flow to hot water tank delta t of 5oc.
    It's been in a year and worked fine, no sign of refrigerant leaks.
    Wondering if it is a faulty expansion valve.
    Ambient was 1oc today but was doing the same at 8oc.
    Have about 20 of these installed all with same parameters and work fine and no problems running hot water up to 48oc

    Thanks for any help



  2. #2
    Join Date
    Jan 2014
    Location
    shetland
    Posts
    18
    Rep Power
    0

    Re: Delonghi r410a Air Source Heat Pump High Pressure problem

    Thanks for the help

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Delonghi r410a Air Source Heat Pump High Pressure problem

    .

    Start with the obvious.

    What is the HP set to?

    Is the water flow through the heat exchanger restricted?

    Is there air in the water side?

    38 bar is about 60 degsC so that is on the upper end of hot for
    water flow at 50 degsC. What is the temp difference over the
    heat exchanger?

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..