    Modeling a Condenser



    Hi guys

    im a 3rd year university student (mech engineering) writing a report on a refrigeration system.

    i need to model a condenser.
    i have the real life version working, but i need to get the numbers to match.

    so i started to look at it as a heat exchanger problem.

    real:
    --------------R134a------------Air-----
    mass flow------?????----------0.06136kg/s
    cp-------------?????----------1005kJ/KG k
    T in -----------35c------------20c
    Tout----------17.1c------------?????

    its a 20 tube pass (20mm tubes) with the where the tubes are 120mm long.
    so i get the area to 7.53e-4 m2
    U = 425
    and i removing 442W of heat.

    but the log mean temp difference comes out @ 2640*C

    (base on log mean temp = Q/U.A)

    which obviously isnt right.

    so i decided to try and work out the mass flow and cp for the refrigerant and work it 'from the other way'

    cp = 0.857kJ/kgk
    http://www.airliquide.com/en/busines....asp?GasID=141
    but thats @ 25*C and 1 bar, not 35C and 12 bar

    i calculated the mass flow to be 4.1637e-3 kg/s
    based on darcy's equation for a 1.95m cap tube @ 0.66mm dia causing a pressure drop of 11 bar, that got me the velocity, then i multiplied by the density (again at the wrong pressure/temp)

    so my question(s):
    is there any way to accuratly calcuate the mass flow of refrigerant?

    does any one know the cp and density of R134a @ the correct conditions, or any way to work it out?

    am i competely wrong on my entire approach

    cheers
    targ



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Modeling a Condenser

    I don't see any information on the fin pack (fin pitch and material). I don't understand the tube pitch as well. Is the fin pack 20 tubes high with 20mm wide tubes?
    How many rows?
    Is the fin pack as long as the pipes (120mm)?
    Also: how is it the refrigerant is colder than air when leaving the condenser

  3. #3
    Join Date
    Apr 2006
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Modeling a Condenser

    ok sry

    20 rows of 20mm tube. the tube pack is 240mm high by 120mm wide (the tubes are horizontal)

    the fins are steel, as are the tubes.

    they are vertical, 2mm thick there is 76 across the 120mm width. and they are 75mm deep.

    does that make any sense/help?

    cheers
    targ

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Modeling a Condenser

    No, there's something wrong.
    How many tubes in vertical? If the coil il 240mm high, and the tube pitch is 20mm, it means that there are max 12 tubes in one row, but if the tube is 20mm dia. that leaves no space for air.
    you probably mean 9.35mm (3/8") dia pipe on a 20mm or 25 mm pitch. That would result in a 6 tubes in vertical and let's say 3 to 4 rows across.
    Then: fins can't be 2mm thick. They are maybe 0.1mm thick and 2mm pitch.
    Finally: 76 fins x 2mm pitch makes a total 152mm wide coil, and not 120mm, let alone the frame.
    Last edited by NoNickName; 19-04-2006 at 01:54 PM.

  5. #5
    Join Date
    Apr 2006
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Modeling a Condenser

    right ive decided to draw a pic, as obviously i can explain well enough.

    http://img507.imageshack.us/img507/9460/73104op.jpg

    thats NOT my condenser, thats what a google image search came up with, ive anotated to show what i was trying to say.

    any more questions?

    cheers
    targ

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Modeling a Condenser

    Ok, that's a single row, 6 tubes coil, 3/8" tube dia, 25mm tube pitch, 0.1mm fin thickness and more or less 3mm fin pitch.
    Does your coil like like that, but with 20 tubes and 76 fins? If yes, it will be 25mm pitch x 20 tubes=500mm high, and 76 fins x 3mm fins pitch = 228mm wide.
    One row is approx 25 mm deep.
    Your coil is then 500x228x25 mm

  7. #7
    Join Date
    Apr 2006
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Modeling a Condenser

    Quote Originally Posted by NoNickName
    Ok, that's a single row, 6 tubes coil, 3/8" tube dia, 25mm tube pitch, 0.1mm fin thickness and more or less 3mm fin pitch.
    Does your coil like like that, but with 20 tubes and 76 fins? If yes, it will be 25mm pitch x 20 tubes=500mm high, and 76 fins x 3mm fins pitch = 228mm wide.
    One row is approx 25 mm deep.
    Your coil is then 500x228x25 mm
    yes!
    thats it.

    targ

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Modeling a Condenser

    That resolves into

    Internal coil volume 0.3232 liters
    Total exchange surface 1.55 sqm
    Air side exchange coefficient 4022 W/sqm K
    Global exchange coefficient 22.74 W/sqm K
    LMTD 11.97°C
    Air entering leaving 20/24.9°C
    Refrigerant entering 35°C
    Refrigerant flow rate 7.78 Kg/h
    Cooling capacity 420W
    Air flow 260 m3/h

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Modeling a Condenser

    Quote Originally Posted by Targ
    so i decided to try and work out the mass flow and cp for the refrigerant and work it 'from the other way'
    Hi Targ,
    You cannot just use the specific heat of the fluid since this is a phase change process also. For any given mass flow you have both sensible and phase changes occurring in the condenser (also the evaporator).

    The vapor exiting the compressor is superheated to a high temperature.

    The sensible component of the total heat exchange is as you described it: mass flow X Cp X dT (temperature difference between the discharge temperature and the dew point temperature of the refrigerant at condensing pressure).

    The phase change component of the total heat exchange process is: mass flow X dh (enthalpy difference between x=1 and x=0 on a Mollier diagram (log P-H diagram for the refrigerant)

    Total Q = sensible + Phase change

    The total heat exchange should balance with the energy transfer to the air circulated as: Mass flow (air) X Cp X dT (temperature difference between entering and leaving air from the condenser)

    Does that help you?

  10. #10
    Join Date
    Apr 2006
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Modeling a Condenser

    Quote Originally Posted by NoNickName
    That resolves into

    Internal coil volume 0.3232 liters
    Total exchange surface 1.55 sqm
    Air side exchange coefficient 4022 W/sqm K
    Global exchange coefficient 22.74 W/sqm K
    LMTD 11.97°C
    Air entering leaving 20/24.9°C
    Refrigerant entering 35°C
    Refrigerant flow rate 7.78 Kg/h
    Cooling capacity 420W
    Air flow 260 m3/h

    thank you very much, but can you explain where/how you worked this out??

    thats nearly excalty what im seeing in real life, so if i can write that up i will be forever indeted to you

    cheers
    targ
    Last edited by Targ; 19-04-2006 at 10:00 PM.

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Modeling a Condenser



    So, I use a coil manufacturer selection program.
    Because I don't bother, and my place practice is more valuable than theory.

  12. #12
    Join Date
    Apr 2006
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Modeling a Condenser

    what is the name of this mythical program?

    many thanks for your efforts.
    targ

    I do love that quote.

  13. #13
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Modeling a Condenser

    www.stefani-online.it

    I don't remember if you can directly download the software or have to ask for a license unlocking code, which is free nonetheless.

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Modeling a Condenser

    Where's the link for the software selection program please?
    Is it a large file to post?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Apr 2005
    Location
    Adelaide
    Age
    54
    Posts
    10
    Rep Power
    0

    Re: Modeling a Condenser

    Mass Flow (m) = Refrigeration capacity of 1 Kw (Qe) / Refrigeration Affect (qe)

    Refrigeration Affect (qe) = Hc-Ha (on a PH chart this)
    Hc = enthalpy of 134a at your saturaterd suction temp
    Ha = enthalpy of 134a at your saturaterd discharge temp

    this divide by 1Kw will give you as mass flow rate of refrigerant per kilowatt in Kg/s

    Alternativly mass flow can be calculaterd by
    Mass Flow rate (m) = Piston displacement (Vp) x Density (p)
    Density(p) is needs to taken your saturaterd suction temp (SST)

    Hope this helps

  16. #16
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Modeling a Condenser

    Quote Originally Posted by Peter_1
    Where's the link for the software selection program please?
    Is it a large file to post?
    Yes, it is big. Sorry, it can't be downloaded, probably they restructured the website.
    Feel free to ask them.

  17. #17
    Join Date
    Apr 2006
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Modeling a Condenser

    i have email them to no response.

    does anyone know where or how i can model future condensers.

    as i think this software or something like it could be extremely useful for the future.

    or even if some one knows the theory behind this or has a link, ill try and write my on program.

    cheers
    targ

  18. #18
    Join Date
    May 2006
    Location
    Xi an, China
    Age
    51
    Posts
    65
    Rep Power
    18

    Re: Modeling a Condenser

    Quote Originally Posted by NoNickName
    That resolves into

    Internal coil volume 0.3232 liters
    Total exchange surface 1.55 sqm
    Air side exchange coefficient 4022 W/sqm K
    Global exchange coefficient 22.74 W/sqm K
    LMTD 11.97°C
    Air entering leaving 20/24.9°C
    Refrigerant entering 35°C
    Refrigerant flow rate 7.78 Kg/h
    Cooling capacity 420W
    Air flow 260 m3/h
    Compare to my calculation:

    Internal coil volume 0.3277 liters
    Total exchange surface 2.36 sqm
    Ref side exchange coefficient 1558 W/sqm K
    Air side exchange coefficient 27.68 W/sqm K
    Average LMTD 10.06°C
    Air entering leaving 20/24.77°C
    Refrigerant entering leaving 35/23.95°C
    Refrigerant flow rate 7.78 Kg/h
    Cooling capacity 417W

    Tube: copper, Fin: Aluminum; both steel cause little difference

  19. #19
    Join Date
    Apr 2006
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Modeling a Condenser

    Quote Originally Posted by autt
    Compare to my calculation:

    Internal coil volume 0.3277 liters
    Total exchange surface 2.36 sqm
    Ref side exchange coefficient 1558 W/sqm K
    Air side exchange coefficient 27.68 W/sqm K
    Average LMTD 10.06°C
    Air entering leaving 20/24.77°C
    Refrigerant entering leaving 35/23.95°C
    Refrigerant flow rate 7.78 Kg/h
    Cooling capacity 417W

    Tube: copper, Fin: Aluminum; both steel cause little difference
    can i ask how you calculated this?

    many thanks
    chris

  20. #20
    Join Date
    May 2006
    Location
    Xi an, China
    Age
    51
    Posts
    65
    Rep Power
    18

    Re: Modeling a Condenser

    I calculated that use my program.

    I check my input, a 2mm fin pitch results to 419W cool capacity, 3mm pitch results to 411W, should I doubt myself??

    In my program, a condenser is devided into 3 region along duct flow: super heating, two phase and super cooling section, which have different heat transfer equation.

    First, suppose ref side outlet state, i use the state that ref dryness=0 and super cooling temperature=0; then use both side heat transfer to calculate three section tube length, get a new suppose state by comparison to real length, iterate the calculation to a satisfied precision.

    Vertical and horizonal ref flow coil use different LMTD and two phase heat transfer coefficient calculation equation.

    There are so much to explain my calculation so i suggest you look up articles about heat transferation needed in a condenser, such as single and two phase, finned surface heat transfer coefficient or mechanism. After trying your calculation, you will find more.

  21. #21
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Modeling a Condenser

    As far as I understand, I see extrme diffrences in what Autt calculated and what NoNickName calculated.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  22. #22
    Join Date
    May 2006
    Location
    Xi an, China
    Age
    51
    Posts
    65
    Rep Power
    18

    Re: Modeling a Condenser

    Quote Originally Posted by Peter_1
    As far as I understand, I see extrme diffrences in what Autt calculated and what NoNickName calculated.
    Air side exchange coefficient 4022 W/sqm K
    Global exchange coefficient 22.74 W/sqm K


    Ref side exchange coefficient 1558 W/sqm K
    Air side exchange coefficient 27.68 W/sqm K


    Do you mean this? I can affirm that air side heat exchange coefficient should not be so big, normally it should no more than 100, it will be very small in this case by that air speed is as slow as 0.64m/s in calculation, I think NoNickName just miswrite it, it should be a ref side value.

    Different suggested ref side exchange coefficient equations get varies value but cause small difference in air cooling condenser, for air side has the main heat resistance, so the total pricision mainly relies on air side calculation, fortunately it can be done well.

    cheers

  23. #23
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Modeling a Condenser

    Hi,

    Quote Originally Posted by Peter_1
    As far as I understand, I see extrme diffrences in what Autt calculated and what NoNickName calculated.

    I believe Peter_1 mean about this:

    NoNickName = Cooling capacity = 420 W
    Autt = Cooling capacity = 417 W

    Try to imagine if they express capacity in eV (electronvolt)

    Best regards,

    Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  24. #24
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Modeling a Condenser

    Sorry, wrong read/interpreted.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  25. #25
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Modeling a Condenser

    My mistake.
    Though ref and air side coeff. change in relation to geometry, pitches, etc.

  26. #26
    Join Date
    Apr 2006
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Modeling a Condenser

    does any one have useful links or articales i could read, as this topic is bugging me that i dont get it.

    and i can find a program to calculate if for me, and they must be out there some where.

    cheers
    targ

  27. #27
    Join Date
    May 2006
    Location
    Xi an, China
    Age
    51
    Posts
    65
    Rep Power
    18

    Re: Modeling a Condenser

    Here is a pdf link for heat transfer
    http://www.sae.org/altrefrigerant/pr...esw-mathur.pdf

  28. #28
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Modeling a Condenser

    Hi autt,

    That was an excellent resource you posted.

    Thank you.

  29. #29
    Join Date
    Apr 2006
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Modeling a Condenser

    Quote Originally Posted by autt
    Here is a pdf link for heat transfer
    http://www.sae.org/altrefrigerant/pr...esw-mathur.pdf

    thanks that seems to outline the whole area very well, and should give plenty to work from.

    many thanks
    targ

Similar Threads

  1. Condensor split temperature
    By Peter_1 in forum Fundamentals
    Replies: 14
    Last Post: 31-07-2011, 05:49 PM
  2. method to design air cooled condenser
    By abbasi in forum New Technologies
    Replies: 4
    Last Post: 12-02-2008, 08:34 AM
  3. Optimum condenser fan speed
    By star882 in forum Fundamentals
    Replies: 4
    Last Post: 27-02-2006, 01:50 AM
  4. Cooling condenser of split with condensate from evaporator
    By smileypete in forum Air Conditioning
    Replies: 11
    Last Post: 10-07-2005, 08:21 AM
  5. Condenser Fan
    By Vicky in forum Supermarket Refrigeration
    Replies: 3
    Last Post: 20-04-2005, 08:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •