26-11-2014, 06:26 PM #1
Trane - Adaptive control - Stopped
Hello !
I have Trane chiller which i cannot run .
The machine show message : ''Stopped by Ext Source "
The controller is : Trane Adaptive Control
Anyone know how can i unlock it ?
-
26-11-2014, 10:27 PM #2
Re: Trane - Adaptive control - Stopped
What external controls are attached to the machine?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
27-11-2014, 07:38 AM #3
Re: Trane - Adaptive control - Stopped
Hello !
The machine is disconnected and there is no other controls as i can see .
I attach few photos here
1183069.jpg
1183069-2.jpg
1183069-3.jpg
-
27-11-2014, 07:56 AM #4
Re: Trane - Adaptive control - Stopped
I attach the message
DSC01986.jpg
DSC01985.jpg
DSC01984.jpg
-
27-11-2014, 08:22 PM #5
Re: Trane - Adaptive control - Stopped
flow switch interlock or remote start/stop signal open circuit
-
27-11-2014, 08:43 PM #6