    Sporlan LAC-10 with remote bulb. Where to install the bulb?



    I have system with R410A & it must work in winter ambient conditions. A ordered Sporlan LAC-10-295 and in comes with a remote bulb. So i have no idea where to put the bulb, because the datasheet says, that care should be taken but... no information on bulb location: which pipe? I suggest liquid return from the condencer, but have no explanation for myself.

    Does anybody know or have experience with it?



  2. #2
    Join Date
    Jul 2013
    Location
    Russia
    Age
    38
    Posts
    3
    Rep Power
    0

    Re: Sporlan LAC-10 with remote bulb. Where to install the bulb?

    Meanwhile i got reply from Sporlan:

    The bulb should be placed in location that will provide a constant ambient temperature of about 80F. These are air charged valves. They do not rely on the bulb to sense any temperatures for operation. See the first paragraph on page 35 of the R410 catalog.

    So the case is closed

  3. #3
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    306
    Rep Power
    14

    Re: Sporlan LAC-10 with remote bulb. Where to install the bulb?

    Thanks for sharing!

    The page 35 says:
    Special consideration needs to be taken when utilizing valves with
    remote bulbs. Because of the air charge, these models are affected
    by ambient temperatures at the remote bulb. (Although the remote
    bulb is affected by ambient temperature, it is strictly a pressure
    regulating valve and not a temperature control device.) Therefore, it
    is necessary to locate the remote bulb in as nearly constant ambient
    as possible to maintain a constant pressure setting. For example, the
    remote bulb located in the return air can be used. Since these models
    are set in 80F (26.7C) ambient, any appreciable variation from this
    temperature will cause the pressure setting to vary. The actual pres-
    sure setting change is 1 psi (0.069 bar) for every 7F (3.9C) increase
    or decrease in the ambient temperature.
    Last edited by narkom; 26-11-2014 at 04:29 PM.

  4. #4
    Join Date
    Nov 2014
    Location
    FRANCE
    Age
    24
    Posts
    1
    Rep Power
    0

    Re: Sporlan LAC-10 with remote bulb. Where to install the bulb?

    thanks for your share of the article.


    ________________________________________________
    etui iphone 6 housse iphone 6
    Last edited by wovnron; 28-11-2014 at 08:42 AM.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •