    R410A Piping Distribution System - Pressure Test rating



    Hi,

    I'm currently involved in the installation of 38AP Carrier units that utilizes R410A.

    Question:

    Is there any pertinent document that can be used to "justify" the use of 600 and 300 psig on the test (beyond that of the manufacturers documentation)? A code perhaps? A recent ruling?


    I've been using pressure test of 600psig (hi-side) and 300psig (lo-side) for the piping system for most of my R410A installations (in particular for VRF multi system - TOSHIBA SMMSi if you may) - which, is as recommended by TOSHIBA themselves.
    Im being chased for such documents that was raised recently by our principals.

    If anyone here knows of any, please let me know, It'll be a great help.

    Thanks



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: R410A Piping Distribution System - Pressure Test rating

    How do you stop the low side reaching 600psig when you test the high side?

    Not sure of any 'codes' or 'rulings' in the Philippines. In the UK we work to the Pressure Equipment Directive and BS EN 378, as well as the manufacturers recommendations

  3. #3
    Join Date
    Jan 2007
    Location
    australia
    Age
    46
    Posts
    49
    Rep Power
    0

    Re: R410A Piping Distribution System - Pressure Test rating

    You don't... When you pressurise the system it should be equal on both sides of the system, pressure test to 450psi is adequate to check pipe work welds.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: R410A Piping Distribution System - Pressure Test rating

    Looking at the Standards in your country is a liitle open ended.

    They recommend installation in. Accordance with the manufacturers instructions and later in the document state using 300psi for leak testing. I couldn't find specifics on stength testing though.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: R410A Piping Distribution System - Pressure Test rating

    Quote Originally Posted by frank View Post
    How do you stop the low side reaching 600psig when you test the high side?
    If on test are only piping, than easy!
    They are separated.

    To OP:

    Here in EU strenght test is done with pressure of nitrogen equall to 1.43 times of maximum pressure expected in parts of circuit.

    In my area that mean 55°C of condensation temperature.
    That converted to R410A saturation pressures mean around 35 Bar.
    Multiply that with 1.43 and you get 50 Bar test pressure.

    50 Bar = 725 PSI

    If you have 2 pipe distribution system, than both pipes are "condensation" pipes and both pipes should be tested at that pressure for strenght test after brazing of network is done.

    If you have 3 pipe system, than 1 pipe is always low pressure side and strength test could be adjusted to highest expected outdoor ambient temperature at standstill periods.

    From my erratic memory, Mitsubishi Heawy Industries Installation manual for KX4 stated 47 Bar pressure test for all pipes.
    Last edited by nike123; 22-11-2014 at 08:59 AM.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: R410A Piping Distribution System - Pressure Test rating

    What about the term hydrostatic pressure of 1.43 under PED?
    You have the muliplier 1.43 but also 1.25!?

    corresponding to the maximum loading to which the pressure equipment may be subject in service taking into account its maximum allowable pressure and its maximum allowable temperature, multiplied by the coefficient 1.25 or the maximum allowable pressure multiplied by the coefficient 1.43 whichever is the greater

    Pressurizing with nitrogen at 50 bar is in fact very dangerous when something breaks during this test.
    Therefore a hydrostatic test is much better but is practically seen as good as impossible.

    Daikin states 41 bar as far as I remember on indoors and connecting lines.
    Same for M.E. We test at 41 bar during more than a day.
    Last edited by Peter_1; 23-11-2014 at 02:57 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: R410A Piping Distribution System - Pressure Test rating

    Quote Originally Posted by Peter_1 View Post
    Pressurizing with nitrogen at 50 bar is in fact very dangerous when something breaks during this test.
    Therefore a hydrostatic test is much better but is practically seen as good as impossible.
    Hydrostatic test is applicable in manufacturing process. On site, not much, therefore you should use all precaution measures to avoid accidents.


    Daikin states 41 bar as far as I remember on indoors and connecting lines.
    Same for M.E. We test at 41 bar during more than a day.
    I told you that I have erratic memory!

  8. #8
    Join Date
    Jan 2010
    Location
    Philippines
    Posts
    8
    Rep Power
    0

    Re: R410A Piping Distribution System - Pressure Test rating

    Ok, it seems theres no common denominator in the field of standardization of pressure test/leak test of refrigerant system distribution piping (unit coils not included) for R410A - such reason that I was asking if theres any whitepaper outside of manufacturers recommendations that has already set these test parameters.

    Now the lines (lo/hi) will be tested separately based on my statement at the top - thats fixed and it will be done (based on AS 1677.2). The thing I wanted to check is whether the 600psig on the Hi side and 300 on the Low Side is acceptable and theres a paper/code/ratification that says it is what it is and should be, coz frankly the carrier manual dont say any, so i'm lookin at other references. The only ruling we use locally here is what is as stated in pertinent HVAC codes which frankly i cant find any for the R410A systems.

    thats what I was actually searching for.... (Y)

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: R410A Piping Distribution System - Pressure Test rating

    Quote Originally Posted by remwel View Post
    Ok, it seems theres no common denominator in the field of standardization of pressure test/leak test of refrigerant system distribution piping (unit coils not included) for R410A - such reason that I was asking if theres any whitepaper outside of manufacturers recommendations that has already set these test parameters.
    ...
    Yes there is, we have the PED. Do a Google search for "PED 1.43"
    But this PED is not applicable for your country I guess.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: R410A Piping Distribution System - Pressure Test rating

    I always test at 55 degrees condensing equivalent temperature, so I'm with Nike 123, as I understand it EU machines are designed to 55c, but there's no way I would test at 50 bar even if the manufacturer wants it.