    Cool Daikin C5 fault but what unit



    Hello Gents
    I have a C5 fault showing on a controller that runs two ceiling cassettes so an r3t thermistor fault is likely how can I tell which unit is faulty, they are both short cycling on heating before the pre heat sign shows on controller I've read about checking ohms reading against temp on thermistor plug ie 20 deg c = 24.45 k - Ohms but where am I taking the temp reading from for a comparison. your knowledge and help is appreciated
    Last edited by marvyn; 19-11-2014 at 04:08 PM.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Daikin C5 fault but what unit

    Which type of ceiling cassettes? You should locate R3T on the indoor PCB (it's marked on the PCB in white markings) at 20°C, you should meausere 25 kohm, 22.85 at 22°C and 27.41 at 18°C.
    Connect eventually a resistor with a vlau between 40 kOhm and 20 kOhm to test it.
    A decadebox is a good device for this.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Jul 2012
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Daikin C5 fault but what unit

    Should show the unit number 0 or 1 with the fault code , use mode 43 if you need to check which unit is 0 and 1

  4. #4
    Join Date
    Jun 2014
    Location
    london
    Age
    58
    Posts
    10
    Rep Power
    0

    Re: Daikin C5 fault but what unit

    Gsracer the units are not marked up so when in mode 43 what's telling one from the other

  5. #5
    Join Date
    Jun 2014
    Location
    london
    Age
    58
    Posts
    10
    Rep Power
    0

    Re: Daikin C5 fault but what unit

    Cheers fellas the Model is FXFQ5OP7VEB couple of more quickies for you both Peter am I getting my temp measurement from the ambient return air or air off or from somewhere on the pipe work

  6. #6
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Daikin C5 fault but what unit

    The temperature you are measuring is whatever the probe is reading. In this case you are reading the larger pipe temp. If the unit has been off for a while or perhaps on fan only then you should be pretty much near room temperature.

    If you use mode 43 then the fan should spin round when you select each unit thereby letting you know how they are addressed.
    If it gives you jip then might be easier to read ohms from both units, save the farting about, unless of course you like to fiddle.
    Last edited by Tayters; 20-11-2014 at 12:17 AM. Reason: Said coil, meant larger pipe, but I still call a spade a spade. :-)
    Health and safety first..........unless I'm in a hurry.

  7. #7
    Join Date
    Jun 2014
    Location
    london
    Age
    58
    Posts
    10
    Rep Power
    0

    Re: Daikin C5 fault but what unit

    Tayters great help that mate much appreciated

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Daikin C5 fault but what unit

    R3T is connector X17A on the PCB. Disconnect thermistor before measuring.
    R1T = X13A
    R2T = X12A