    Daikin cassette R3T removal replacement



    Hello Gents,
    could some one please give a brief out line how to replace an R3T thermistor on a daikin ceiling mounted cassette basically where does the cable go how do I get to it
    many thanks in advance



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin cassette R3T removal replacement

    The wiring diagram on the electrical cover should show you where R3T connects on the PCB.

    Then just follow the wire.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2014
    Location
    london
    Age
    58
    Posts
    10
    Rep Power
    0

    Re: Daikin cassette R3T removal replacement

    Thanks Brian have got pcb end no problem was wandering how much disassembling was needed to find the other end where it connects to coil can I get to it above ceiling is there an access panel for example where do I attack
    Last edited by marvyn; 18-11-2014 at 09:43 PM.

  4. #4
    Join Date
    Jun 2014
    Location
    london
    Age
    58
    Posts
    10
    Rep Power
    0

    Cool Re: Daikin cassette R3T removal replacement

    Thanks Brian have got pcb end no problem was wandering how much disassembling was needed to find the other end where it connects to coil can I get to it above ceiling is there an access panel for example

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin cassette R3T removal replacement

    full strip down inc removal of electrics and drip tray, ideally the fan impellor too so you can get ur head in to see

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin cassette R3T removal replacement

    Trying hard to rack my brain here so could be around.

    Some dismantling is going to be required so a cross head screwdriver, a spanner and maybe a bucket also.

    Turn if the power.
    Remove the air inlet grille and filter.
    In one of the bottom corners you should find a rubber bung. With the bucket underneath it remove the bung to drain any water that may be in the drain tray.
    If the is a fan guard, remove that.
    Remove the electrical cover and any screws holding the box as well.
    Unscrew and remove the fan inlet shroud.
    Now undo the nut holding the fan on, pull the fan out and put the nut back on that you don't lose it.
    In one corner there should be a detachable metal plate or boxing giving access to the condensate pump and hopefully the ends of the coil where the sensor will be.
    Or
    Look on the outside on the unit above the ceiling to see if there is an access cover there - perhaps do this first

    If things still don't look good then you may need to remove the front fascia, don't forget to catch the ceiling as the fascia often provides support. After that remove the drain tray to get full access to the coil.

    Good luck.
    Last edited by Brian_UK; 18-11-2014 at 10:29 PM. Reason: spelling, of course.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Jun 2014
    Location
    london
    Age
    58
    Posts
    10
    Rep Power
    0

    Re: Daikin cassette R3T removal replacement

    Nice one chaps appreciated

  8. #8
    Join Date
    Jun 2014
    Location
    london
    Age
    58
    Posts
    10
    Rep Power
    0

    Re: Daikin cassette R3T removal replacement

    I have a C5 fault showing on a controller that runs two ceiling cassettes so an r3t thermistor fault is likely how can I tell which unit is faulty, they are both short cycling on heating before the pre heat sign shows on controller I've read about checking ohms reading against temp on thermistor plug ie 20 deg c = 24.45 k - Ohms but where am I taking the temp reading from for a comparison. your knowledge and help is appreciated

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin cassette R3T removal replacement

    Run each unit via the 43 code and tie up which unit has the error code.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Jun 2014
    Location
    london
    Age
    58
    Posts
    10
    Rep Power
    0

    Re: Daikin cassette R3T removal replacement

    Your a gent Brian thanks for your reply