    Dec 2006
    Indonesia
    68
    37
    30C to 20C in one hour?
    Hi all, greetings from Indonesia again...
    I need to calculate how much compressor power needed for this:
    I need to cool 10.000 liter (roughly 2,641 gallon) of water from 30C (86F) down to 20C (68F) within one hour.
    I found this formula:
    BTU = gallons x temperature change x 8.33
    The result for my numbers would be... 395,991 BTU or 155 HP.
    Is that number seems realistic? It seems so high, or is there a mistake?
    Thank you for all your input, really appreciate it.
    Regards,
    Yahya.
    Aug 2010
    110
    8
    Re: 30C to 20C in one hour?
    10000l/hour = 2.8l/sec
    30deg - 20deg = 10deg
    specific heat capacity of water = 4.2
    2.8 x 10 x 4.2 = 117.6kW of refrigerating capacity.
    I don't really know what BTU's and Gallons are?
    Sep 2012
    India
    77
    7
    For getting 120 kW cooling considering 10 C evaporating and 40 condensing temperature refrigeration compressor will need around 20 to 25 kW power input depending upon which refrigerant is used.
    Dec 2006
    Indonesia
    68
    37
    Thank you so much for all the replies, really helps.
    Dec 2006
    Indonesia
    68
    37
    Quote Originally Posted by sandybapat View Post
    May I know how did you came up with the number 20 to 25 kW power input? Thanks.
    Sep 2009
    Iran
    462
    12
    also
    Q= MC (t2-t1)
    M=10000 Kg/ h
    C=1 for water
    Q= 10000 * 1(30-20)
    Q= 100000 cal/h
    1 Kw = 860 cal
    to get that you need to add %10 for safety and then you have to choose your Comp.
    your evaporator temp. about 10 c ( out let temp. - delta T )
    your condenser temp. about (ambient temp. + 10)
    Sep 2012
    India
    77
    7
    As mbc has explained I tried to select compressor 120 kW capacity with 10 deg C evaporation temp and 40 deg C condensing temperature and I got the power consumed by compressor.