    McQuay Air Cooled Chiller



    Hi

    i have a problem with McQuay air cooled chiller
    McEnergy HA 105.2 ST , Carel Microproccessor

    Compressor 1 is not starting up and always there is alarm of : High pressure switch

    i replaced pressure switch and the problem still , i make a bridge shant on it from controller ?!! and the problem still ...

    any one can help with regards

    Waseem



  2. #2
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: McQuay Air Cooled Chiller

    hi your pressure high transducer might need changing or re calibrating ,and also check in settings of trip point setting, some time the connector on the switch has damp or water in it