Equipment for variable temp container
Hi all, needing some advice. We have been asked to fit static equipment to a 9 metre long refrigerated lorry body. The customer wants to be able to run it at fridge or freezer temp depending on the requirement. Obviously this raises problems straight away.
Does anyone have any thoughts on a solution, not really wanting to go down the mono block route.
Thanks
-
13-11-2014, 11:36 PM #2
Re: Equipment for variable temp container
cant see what the issue is, spec it as a freezer and adjust the stat as and when needed
remote condensing unit and freezer[finned]evapIf the World did not Suck, We would all fall off !
-
14-11-2014, 01:06 AM #3
Re: Equipment for variable temp container
as said before spec it as a freezer,the only issue I have encountered is the seals around the doors are bad on truck bodies always make sure the body is 100% level,
-
16-11-2014, 02:59 PM #4
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: Equipment for variable temp container
you should calculate your load for high one (( freezer temp))
and then put crankcase pressure in suction line and set that one to freezer temp .
you should be careful to adjust your T E V ( expansion valve ).
also it is better you use pump down system for shout down.
with thermostat you can set for your room temp.