    Fujitsu



    Hi can any body help with error light's on my Fujitsu AGYG14LVCA / AOYG14LVLA they are timer red 5 times operation 9 times economy continuous flashing and will not work thanks
    Last edited by pcman; 13-11-2014 at 06:29 PM.



  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Fujitsu

    Outdoor unit detected compressor not spinning round as it should.
    You can power the outdoor of for a couple of mins and retry it but more than likely trouble with compressor or inverter that drives it which is part of the outdoor PCB.

    Service manual (not that it helps much...): http://www.fujitsuklima.hu/vmfiles/s...aoyg14lvla.pdf

    Inverter testing: http://www.refrigeration-engineer.co...nveter+testing

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.