    emerson refridgeration unit



    I have an emerson unit it was running and icing up around tev i check gas and found it was short of gas pressure tested and no leak found top up with r407c and unit running ok. After a week checked unit and it had iced up on evaporator coil. Checked tev and filter dryer and both seem ok. Had anyone got any ideas on why this happens and how to resolve it



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: emerson refridgeration unit

    Chiller or Freezer? What sort of defrost system does the system have? Are the door seals and panels in good condition? Is the drain clear?
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Jan 2012
    Location
    West midlands
    Age
    44
    Posts
    33
    Rep Power
    0

    Re: emerson refridgeration unit

    Guessing its a cold room if it's 407c.
    Is the whole of the evap iced or just the start by tev.
    If just the start, sounds short of gas again. Go around with your
    Sniffer while it's still got a charge to give you a rough area.

    If it's all iced yeah drains, defrosts, doors being left open fans ect.

    Bryan

  4. #4
    Join Date
    Jul 2012
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: emerson refridgeration unit

    R407c is a blend, so if it had a leak it's probably not the correct blend any more

  5. #5
    Join Date
    Nov 2014
    Location
    United Kingdom
    Posts
    2
    Rep Power
    0

    Re: emerson refridgeration unit

    Thanks guys. Its a unit in a data centre there is no defrost setting that I have found as its all controlled by a trend system, its iced around 1/4 of coil to tev. I have increased fan speed to help but as there are 2 circuits on system its the 1st one that has faults

  6. #6
    Join Date
    Jan 2010
    Location
    Vietnam
    Posts
    6
    Rep Power
    0

    Re: emerson refridgeration unit

    The PAC not enough refrigerant R407C, may be has leaking on system.