    Reviving old daikin 8kw r22 inverter



    Hi guys, I've pulled out a daikin ac that was in working order before a circular saw was put through the pipework by accident during a Reno...
    I walked the owner through closing off the service valves so the outdoor unit didn't get any debris lodged in it.
    It has absolutely no gas. I happen to have a ready supply of reclaimed r22.
    My question is, should I replace/top up the compressor oil?
    The unit was running fine up until the day it was forcibly degassed.
    Obviously I have the means to weigh in the correct charge, being inverter, it must be weighed in...

    Cheers guys

    Sparkletron
    Last edited by Sparkletron; 10-11-2014 at 10:17 AM. Reason: Spelling



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Reviving old daikin 8kw r22 inverter

    If the valves were closed soon after the pipes were cut then it should be OK.

    Very little oil would have been lost.
    Brian - Newton Abbot, Devon, UK