Thread: VRF mechanical code conflict
06-11-2014, 04:20 PM #1
Come Jan 1, 2015 it will be very difficult/impossible to install VRF equipment in New York City due to a change in the Mechanical code. No refrigerant lines can pass through a space that can be occupied, connected to a system with more than 10 pounds of refrigerant. This is due to their interpretation of Ashrae 15 safety guidelines. Is anyone out there seeing something like this ?
06-11-2014, 07:44 PM #2
Re: VRF mechanical code conflict
Water chillers it is then !
06-11-2014, 09:35 PM #3
Hi Ralph
Can't say I'm familiar with Ashrae 15, as we work to different standards over here - BS EN 378.
Do you have a link to the code so we can have a look and comment?
06-11-2014, 10:06 PM #4
I think that you may be misinterpreting the standard.
It seems that you are now limited to 10lbs/1000sq.ft. so you need to calculate your total charge and see if it can leak into the smallest area that the leak may occur in.
Info gleaned from here..
https://www.google.co.uk/url?sa=t&so...U8NMkyS15YvVbA
07-11-2014, 11:38 PM #5
07-11-2014, 11:46 PM #6
I have seen this trane publication. From what I understand Ashrae 15 does not take into o account the refrigerant is heavier than air. I would like to send you what I have but don't know where to send it to or where to post it.