    Come Jan 1, 2015 it will be very difficult/impossible to install VRF equipment in New York City due to a change in the Mechanical code. No refrigerant lines can pass through a space that can be occupied, connected to a system with more than 10 pounds of refrigerant. This is due to their interpretation of Ashrae 15 safety guidelines. Is anyone out there seeing something like this ?
  2. #2
    Join Date
    Nov 2008
    Location
    scunny!
    Age
    30
    Posts
    302
    Rep Power
    17
    Re: VRF mechanical code conflict
    Water chillers it is then !
  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,130
    Rep Power
    43
    Hi Ralph
    Can't say I'm familiar with Ashrae 15, as we work to different standards over here - BS EN 378.
    Do you have a link to the code so we can have a look and comment?
    I'm back on the Pale
  4. #4
    Brian_UK's Avatar
    Brian_UK is online now Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    70
    Posts
    10,681
    Rep Power
    52
    I think that you may be misinterpreting the standard.
    It seems that you are now limited to 10lbs/1000sq.ft. so you need to calculate your total charge and see if it can leak into the smallest area that the leak may occur in.
    Info gleaned from here..
    https://www.google.co.uk/url?sa=t&so...U8NMkyS15YvVbA
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
    Please support http://the100project.net/Home
  5. #5
    Join Date
    Aug 2002
    Location
    florida
    Posts
    24
    Rep Power
    0
    Quote Originally Posted by frank View Post
    Hi Ralph
    I don't have a link but I do have a copy. Can I send to you and you post ?
  6. #6
    Join Date
    Aug 2002
    Location
    florida
    Posts
    24
    Rep Power
    0
    I have seen this trane publication. From what I understand Ashrae 15 does not take into o account the refrigerant is heavier than air. I would like to send you what I have but don't know where to send it to or where to post it.