    Daikin ry200f7w1



    Hello everyone. Sorry for my English in advance. I have a trouble with DAIKIN RY200F7W1. 20141029_141829.jpg. Controller remote shows H3 error. PCB LEDs in outdoor unit show that it is sensor system fault.I can't launch it in any mode. I tried to make short-circuits with pressure sensors but it gave no results. Short-circuits with thermal sensors I haven't made because I don't know their nominal value. Here is the principal circuit's photo:20141029_142646.jpg. I have no manual on it. Thanks in advance.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Daikin ry200f7w1

    H3 is activation of the high pressure switch or possibly a PCB fault.

    If the unit will restart after a power off then check the operating pressures when running.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Nov 2014
    Location
    Ukraine
    Age
    38
    Posts
    3
    Rep Power
    0

    Re: Daikin ry200f7w1

    Hello Brian. I tried to restart it and made a short circuits with both high pressure's contact on pcb but it was in vain. Do you know where can I get a principal circut on it more detailed than that. And one more question: is there any book about split systems conditioners. Thank you.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin ry200f7w1

    h3 hp trip over 33 bar open circuit resets under 24 bar- unplug h1p and test continuity- or when powered up test mains voltage (live) in and out- also check soldered joints on pcb- you should have mains voltage in and out h1p lp switch, fan thermistors q1q2 overload(comp contactor)
    condenser fan will operate at diffrent speeds, moniter operation of fan for 20 mins whilst monitering operating pressures
    does this trip in heating or cooling mode?

  5. #5
    Join Date
    Nov 2014
    Location
    Ukraine
    Age
    38
    Posts
    3
    Rep Power
    0

    Re: Daikin ry200f7w1

    Thanks all for help.I replaced pcb with the same one, and it started to work properly. Now I'm thinking where it's possible to get the enough detailed principal circut scheme to fix the pcb. Does anyone knows methods suitable for repairing pcb.