    Linde Packs



    Has anyone any input as to why most of the packs designed and built by Linde do not contain oil seperators. This applies to LT & HT applications.



  2. #2
    spencerroberts's Avatar
    spencerroberts Guest
    Linde packs use an oil return method inside the suction accumulator.

    A nominal amount of oil sits in the bottom of the accumulator & is carried down the suction of any running compressor through an 'oil return screw' (protruding from the underside of the accumulator).

    By setting these screws, you can adjust the flow rate.

    Although many question the effectiveness of this gravity system as opposed to the traditional pressurised system, Linde have utilised this design for many years and it works, so long as you have the screws set correctly.

    Linde have a couple of commissioning engineers who are experts with the Linde oil system (namely: **** Early & Alan Barker), if you can get to speak to them.

    Hope this helps.

Similar Threads

  1. Linde Pack, Oil recovery system.
    By buddy in forum Supermarket Refrigeration
    Replies: 26
    Last Post: 05-01-2007, 03:04 AM
  2. Packs Supermarkets and larger plants in Canada
    By Peter_1 in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 11-09-2006, 07:01 AM
  3. Linde Packs !!!!!!!!
    By Latte in forum Supermarket Refrigeration
    Replies: 3
    Last Post: 14-04-2005, 06:51 PM
  4. Sroll Packs [oil Changes]
    By jockfrost in forum Commercial
    Replies: 5
    Last Post: 01-07-2003, 11:46 PM
  5. Liropa Controllers (Linde Fridges)
    By Latte in forum Refrigeration Books
    Replies: 1
    Last Post: 25-02-2003, 09:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •