Carrier 30RA/Ry aircooled chiller
Client has a Carrier 30RA/RY with pro-logic plus control. 2 circuit system, 2 comp circuit A and 3 Comp Circuit B
Is there a way to program controller for compressor start sequence or Circuit start sequence or is this only done by the controller using its compressor run time logic?
-
01-11-2014, 09:54 AM #2
Re: Carrier 30RA/Ry aircooled chiller
Circuit sequence only I'm afraid go into configuration menu then user menu try pass =11 or 88. Unit must be in local off when you configure.
Circuit loading sequence will be set as 1 = auto. 2 = A lead. 3 = B lead.Last edited by Gibbo; 01-11-2014 at 01:06 PM.
-