16-04-2006, 10:36 PM #1
intermittent starting fridge/freezer
Hi guys,
i have a problem with a domestic fridge freezer, namely when the unit is switched on it will click quietly into life, run the compressor for around 5 seconds and then with a loud click will switch off.
With the unit on there is power all the time at the control panel but the compressor only switches on about once every 5-10 mins, like i say for about 5 seconds at a time.
This unit is only 2 years old but is out of warranty, any advice before i purchase a new one would be much appreciated.
cheers
mrmtata
-
16-04-2006, 11:05 PM #2
Re: intermittent starting fridge/freezer
Hi mate,
Sounds like the comp is goosed.
You could try and buy a new starter for it (relay) but it's probebly not worth it.
Try switching it off for 24hours and then test it again.
Make sure there is plenty air flow for the hot bit at the back (condensor).
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
17-04-2006, 04:12 AM #3
Re: intermittent starting fridge/freezer
I would try a 3-in-one start kit before you trash it. Kit cost about twenty dollars or so.
-
17-04-2006, 06:56 AM #4
Re: intermittent starting fridge/freezer
This sounds like the classic case of the R134a blocked capillary
Stat calls, compressor kicks in, runs into a vacuum, no compressor cooling, klixon operates. Compressor then cycles on klixon
-
17-04-2006, 09:11 AM #5
Re: intermittent starting fridge/freezer
Thanks for your ideas, i left the unit off for 12 hrs last night, flicked it on this morning and got the same result. I will try leaving it off for 24 and see what happens.
Frank, re the blocked capillary it this a terminal problem or can it be repaired?
I will look into the 3 in 1 kit.
cheers guys.
mrmtata
-
17-04-2006, 09:47 AM #6
Re: intermittent starting fridge/freezer
Your compressor is faulty Im afraid
-
17-04-2006, 09:50 AM #7
Re: intermittent starting fridge/freezer
Thanks for the advice guys, much appreciated.
cheers.
-
17-04-2006, 04:48 PM #8
Re: intermittent starting fridge/freezer
I believe there are small hydraulic hand pumps for clearing capillaries although I have never used one. If the gas in your fridge is R134a and the capillary is embedded in the insulation panel then it will end up cheaper to buy a new fridge.
R134a tends to wax the oil and block capillaries.
If you have access to a line tap valve and a manifold set then you can easily check to see if the compressor is pulling a vacuum.
-
17-04-2006, 05:15 PM #9
Re: intermittent starting fridge/freezer
let try another way,when it runs does it get the condenser coils hot if so the system sounds o/k and i would go for the relay,or it could be the run winding ,if it runs for a while and the condenser stays cold or cool,bin it,system fault,just as a after thought, if the compressor gets its supply from a PCB board and not a normal t/stat,check it has 240v, sometimes you get low voltage and poor conections that throw you.
-
17-04-2006, 07:08 PM #10
Re: intermittent starting fridge/freezer
lets try another way,when it runs does it get the condenser coils hot
-
18-04-2006, 05:16 PM #11
Re: intermittent starting fridge/freezer
ooooooooer, i read that wrong,though it was longer, naf pot then.
-
05-05-2006, 07:38 PM #12
Re: intermittent starting fridge/freezer
comp nackerd scrap it i had same prob and changed relay worked for 1 week then no go.
Similar Threads
-
starting of defrost time
By pirestani in forum New TechnologiesReplies: 6Last Post: 28-06-2006, 04:11 PM -
freezer section of fridge/freezer has stopped
By roobydoo in forum DomesticReplies: 3Last Post: 30-05-2005, 08:35 PM -
RFI Interference from Fridge/Freezer
By pathfinder in forum Trouble ShootingReplies: 6Last Post: 19-03-2005, 11:50 AM -
Starting a compressor, and receiver questions.
By DaBit in forum Technical SpeculationsReplies: 9Last Post: 24-08-2002, 12:37 PM -
Intermittent Compressor Rotor Stall (LRA) Symptoms
By JONAH in forum Trouble ShootingReplies: 8Last Post: 26-03-2002, 10:43 PM