Thread: BOCK Pack system oil problems
29-10-2014, 05:40 AM #1
Hi all, I have and BOCK Pack with 3 semi sealed comp. on and it is having problems with oil return from oil separator ( Henry C 9210 ). Can the flout valve in oil separator be faulty.
29-10-2014, 09:19 PM #2
Re: BOCK Pack system oil problems
30-10-2014, 11:45 PM #3
Hi Johann
It could be a leaky float assembly or the needle orifice could be blocked with ferrous particles. Often fine metallic particles from the compressor castings can get pumped into the oil seperator and tend to accumalate around the needle orifice causing a blockage. If it has a removable float assembly take it out and clean it, or replace it.
31-10-2014, 01:16 AM #4
Could also be that separator is undersized for peak flow rates and oil is not separating. I have also had ball floats with holes in them so do not float. Strip it out and inspect.
05-11-2014, 06:40 AM #5
Thanks will try it because klients don,t want to pay