    Cool No visible level in refrigerant site glass.



    We recently delivered a brand new YVAA air cooled chiller to a big site locally. After the delivery the main contractors representative called to say there must be a leak on the chiller and we must come immediately and have a look. His reasoning being that he could not see a refrigerant level in the sight glass (Level Glass) mounted on the side of the evaporator. Our glorious leader went down to have a look. The chiller is far from complete no power or even water connections so he fitted a set of gauges took a reading, measured the ambient visually looked over the chiller for possible leaks,oil etc. He then told them that there did not appear to be any problems. However when the BDM went around to talk about payment for delivery they kept insisting that the chiller was not complete as there was no gas inside it as they could not see a level.

    We are not really worried as we are quite confident that when we commission all will be revealed but as things here are very slow here it could quite possibly be a year before that happens.

    Has anyone ever come across such a problem before? What sort of answers were given (please remember builders know everything).


    Thanking everyone in advance!



  2. #2
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: No visible level in refrigerant site glass.

    Pity it's not ammonia - give them a squirt in the face then ask 'em if there is any gas in..

    Request documentation from manufacturer saying that chiller is supplied with refrigerant?

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: No visible level in refrigerant site glass.

    Any excuse by construction company to delay progress payment for equipment delivered to site, is a common problem.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: No visible level in refrigerant site glass.

    Sight glass is to show that refrigerant is dry, it is not a level gauge and if it was it would only be correct when it is running.

    Tell them that if they do not pay up then the chiller will be removed from site and the client told that any delays are due to their contractor being in breach of contract terms.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Aug 2010
    Location
    UK
    Posts
    110
    Rep Power
    14

    Re: No visible level in refrigerant site glass.

    Theoretically we are the manufacturer, or rather there knowledgeable local agent

  6. #6
    Join Date
    Aug 2010
    Location
    UK
    Posts
    110
    Rep Power
    14

    Re: No visible level in refrigerant site glass.

    Hello Brian

    This is not the liquid line sight glass but rather the Level Glass on the side of the cooler(evaporator).

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: No visible level in refrigerant site glass.

    Hi Piewie.
    I work on a site where one of our customers has got one of these. Someone does not know what they are looking at!

    The sight glass is in the side of the evaporator (Shell and Tube Falling Film) purely to be able to adjust the charge once the chiller is operational.
    From memory these are more like a Centrif where the liquid refrigerant boils off across the tube bundle.

    Tell then to stop wasting time and power up the unit. All then will be revealed!!

    The refrigerant is not necessarily short just because it is not liquefied and at ambient temperature.
    Someone is trying to be a smart arse!

    In short a level is only visible when operational and loaded correctly!
    Grizzly
    Last edited by Grizzly; 28-10-2014 at 06:05 AM.

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: No visible level in refrigerant site glass.

    Could you weigh the charge out and back in again? (or kick them in the nuts)
    Mostly found in Oxfordshire, UK :)

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: No visible level in refrigerant site glass.

    I would ask to see the qualifications of the main contractors representative to see if he is qualified to make such comments/assumptions.