    City multi trouble



    Ok guys this will be hard to put into words but here goes.
    Working on a pury-p300ygma. Unit is cutting out on 1102 high discharge. Have had 2 mitsi engineers down to look at it and have about 40hours of m-net tool readings. We have changed the oil bypass valve(sv1) as its dumping discharge into suction. So we tought anyway.... Then today changed the 4way valve and checked the check valve. Unit runs ok on cooling but cuts out after 6mins on heating. Any ideas????



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: City multi trouble

    5ltr of petrol and a match?

  3. #3
    Join Date
    Oct 2014
    Location
    Ireland
    Age
    33
    Posts
    43
    Rep Power
    0

    Re: City multi trouble

    Have been very tempted to cut the pipes and kick it off the roof. Im going down 2mara to change the compressor.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: City multi trouble

    make sure you energise the crankcase htr for 24 hrs as the internal bearing needs to expand- otherwise it will give symptoms of a siezed compressor- an old work mate had 3 that were siezed when he started it up- turns out mitsubishi issued a claim that you need 24 hrs - hence the 3 faulty compressors were fine

  5. #5
    Join Date
    Oct 2014
    Location
    Ireland
    Age
    33
    Posts
    43
    Rep Power
    0

    Re: City multi trouble

    Ya i will be running system saturday morning. If it doesnt work i will cry.

  6. #6
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: City multi trouble

    I take it you checked and recalculated the charge?


  7. #7
    Join Date
    Oct 2014
    Location
    Ireland
    Age
    33
    Posts
    43
    Rep Power
    0

    Re: City multi trouble

    Yes frist thing i done, was we cannot make out is y the 1/4" pipe from sv1 can be so hot. The suction to compressor is hot to touch but you can leave your hand on it.(forgot my touch probe)

  8. #8
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: City multi trouble

    Hi, have you sorted it? If not can you upload the monitoring tool data for us to have a look at.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  9. #9
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: City multi trouble

    SV1 and SV2 are your discharge to suction bypass safety valves and by the sounds of it are doing their job if the system is tripping on HP.

    A couple of questions;

    Have you confirmed at what pressures SV1 and SV2 are opening?
    Also have you checked your discharge pressure transducers to confirm they are reading correct?
    Is the refrigerant charge correct?
    Does it work on cooling main and heating main?
    Are the indoor filters and coils clean?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  10. #10
    Join Date
    Oct 2014
    Location
    Ireland
    Age
    33
    Posts
    43
    Rep Power
    0

    Re: City multi trouble

    Its actually high discharge(1102).. How do i upload the m-net data?

  11. #11
    Join Date
    Aug 2013
    Location
    Ireland
    Posts
    1
    Rep Power
    0

    Re: City multi trouble

    Why do you change the compressor if unit is running in cooling? what's your discharge temp - if the suctions hot you are bypassing into LP - 4 way valve (know you said changed already) possibly overheated when replaced?

  12. #12
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: City multi trouble

    Quote Originally Posted by dunmaheadin View Post
    Why do you change the compressor if unit is running in cooling? what's your discharge temp - if the suctions hot you are bypassing into LP - 4 way valve (know you said changed already) possibly overheated when replaced?
    Have you confirmed the discharge transducers are reading correct? The fact that SV1 is opening suggest you have HP trouble?

    Send the log to my email and I'll have a look through and upload it.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  13. #13
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: City multi trouble

    Quote Originally Posted by marc5180 View Post
    Have you confirmed the discharge transducers are reading correct? The fact that SV1 is opening suggest you have HP trouble?

    Send the log to my email and I'll have a look through and upload it.
    Check your email
    The difference between genius and stupidity is that genius has its limits.

    Marc

  14. #14
    Join Date
    Aug 2009
    Location
    england
    Age
    66
    Posts
    31
    Rep Power
    0

    Re: City multi trouble

    As the unit works fine in cooling but problems in heating, check LEV3 in BC box

    Skilts
    Last edited by skilts; 05-11-2014 at 08:31 PM.

  15. #15
    Join Date
    Mar 2014
    Location
    England
    Posts
    32
    Rep Power
    0

    Re: City multi trouble

    Sounds like a check valve issue

  16. #16
    Join Date
    Oct 2014
    Location
    Ireland
    Age
    33
    Posts
    43
    Rep Power
    0

    Re: City multi trouble

    Its been brought to my attention that endoflush was used in this system a few years back and they didnt get what they put in back out. (Approx 5litres still in system i think) i think i have located a blockage in a heat exchanger. Ive turned off that unit ant the system has rang error free for the last week. Hotel closes nxt week for a few months so il be breaking into the system to see what i can find.