    Copeland scroll blowing



    Hi guys

    Looking for a second opinion here.Looking at my local pubs beer cellar.As soon as you turn the isolator on the compressor starts for a split second then trips the breaker.I replaced the power cable as it was knackered thinking it could be due to bad insulation but unfortunately it tripped again.Its a 3 phase copeland scroll.Ive check the windings to earth and they're fine,getting 7.5ohms on each winding and getting all 3 phases out the contactor.Im certain the motor is partially siezed but dot want to order up a £600 compressor only to find it was something I over looked.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Copeland scroll blowing

    Did you measure the insulation resistance to earth with a megger type meter or just your multi meter?

  3. #3
    Join Date
    Jan 2013
    Location
    scotland
    Age
    44
    Posts
    52
    Rep Power
    12

    Re: Copeland scroll blowing

    Just a multi,don't have a megger:-(.Cant even get an amp reading as it goes off to quick.The very last time I reset it and switched the isolator on it didnt even try an start just tripped the breaker.Normally I would just condemn the compressor but the fact it tried to start is making me think twice.Its dead now right enough:-(.

  4. #4
    Join Date
    Dec 2005
    Location
    SCOTLAND
    Age
    51
    Posts
    47
    Rep Power
    0

    Re: Copeland scroll blowing

    Disconnect wiring at compressor motor connections and fit into a connector block and switch on power. measure your voltage to see if your phases are balanced on the connector block. If they are and all else seems ok then its more than likely the comp. I would also check the mains breaker....is it a RCD?

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Copeland scroll blowing

    testing windings to earth without the use of a megger is pointless- test winding resistance, phase to phase with a multimeter no problems, i hope the 7.5 ohm was winding to winding if not your pot is deffo goosed

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Copeland scroll blowing

    Totally agree install monkey.

  7. #7
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Copeland scroll blowing

    .

    You need to prove if it is electrically sound as the others have said
    and as the others have said an insulation tester is the tool for the job.

    If it was seized it would take a few seconds to trip maybe as long as
    10 to 15 seconds if it had a large motor rated overload on it.

    As others have said isolate the electrics at the comp end and then run,
    if it trips the electrics are faulty.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  8. #8
    Join Date
    Jan 2013
    Location
    scotland
    Age
    44
    Posts
    52
    Rep Power
    12

    Re: Copeland scroll blowing

    The 7.5ohms was winding to winding and I did disconnect the wiring from the compressor and had all 3 phases when the contactor pulled in.

  9. #9
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Copeland scroll blowing

    Quote Originally Posted by lorano View Post
    The 7.5ohms was winding to winding and I did disconnect the wiring from the compressor and had all 3 phases when the contactor pulled in.
    Winding to winding seems good but you need to winding to earth.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  10. #10
    Join Date
    Apr 2012
    Location
    FL
    Posts
    38
    Rep Power
    0

    Re: Copeland scroll blowing

    Hello Iorano,
    well you are saying that you have checked the windings to the ground and it was 7.5 ohm. so it seems like you have a shortage and a bad news!!And usually it is hard to catch the contunuity problem with multi meters since they send a low voltage through the loop and you may end up seeing some resistance alhough you have a shortage somewhere.In your case you already had very low ohm(to me below 50 is not good).And if you decide to check it one more time with a megger make sure you set the voltage on the megger 2 or 3 times the nominal voltage of the compressor.And my personal opinion, megger is the best way to check the insulation with the right voltage applied!!!!
    good luck...