    Load Calculation



    Hello, I am looking for another professional opinion for our new walk in freezer. The box is built by Norlake, the dimensions are 11' X 6' 10" x 7' 6" with 4" walls. The ambient box temp. is 110F with the unit on the roof in the northeast. We will be loading around 100lbs a day of food products at around an 85F average temp. We might be in and out of the box 20x a day with minimal time inside the box. Let me know if I can give you any more specs to work with, Thank you.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Load Calculation

    4 inch panel is a bit light for 0.0' F or -18' C should be 150mm or 6 inch.
    4 inch polyurethane is OK , 4 inch polystyrene not so good
    Last edited by Magoo; 23-10-2014 at 01:17 AM. Reason: edit

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Load Calculation

    What"s exactly your question?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Load Calculation

    What product is cooled? What is storage quantity?What is required cool down/congel. time.
    Required panel thickens is at least 6 inch.
    Is the floor insulated and heated below insulation?

  5. #5
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Load Calculation

    At only 100 lbs/day of Freezing Load, the most significant proportion of load is going to be air exchange with that OD Ambient. How big is the door, how is the door controlled and curtained, and how much humidity is associated with the 110-ambient and the 85-product? How are you defrosting? To Clarify: what temperature and humidity will inbound air tend to be at for those internals when the door is open?

  6. #6
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: Load Calculation

    hi
    100lbs food your case named fresh product freezing
    time of processing 12 hours
    you need 5 kw fan coil with 7mm fin spacing
    5kw compressor capacity at -25degree centigrade
    required condenser capacity 8.5 kw