    Msh-ga50vb trouble



    Hi guys, i was working on the above unit today and found the coil freezing over. When the unit was switched from cooling to off the outdoor would continue to pump cold gas in resulting in the unit freezing up. And wouldn't switch to heating mode every time i changed setting. Also am i right in saying that if the indoor is off i should have no signal voltage to the outdoor???



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Msh-ga50vb trouble

    Don't know the unit but has the 'go' signal relay welded on?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2014
    Location
    Ireland
    Age
    33
    Posts
    43
    Rep Power
    0

    Re: Msh-ga50vb trouble

    Its a mitsubishi electric split type unit.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Msh-ga50vb trouble

    http://www.aircon-nara.narod.ru/Mits...50_60_80VB.pdf
    52c contactor in outdoor welded - as brian guessed, take the top lid off the condenser and look at the black thing next to the capacitor- its a non inverter unit with a 12v dc signal on 1,2 terminals, 1 an 3 for reversing valve signal (heating)