    Condenser water inlet & outlet temperature

    hello guys,

    For a cooling tower application how can i calculate the condenser water temperature inlet & outlet? i read that there is a book named black book i think they introduce many graphs with different flow capacities, inlet temp, outlet temp, wet bulb temp...... i wanna know how we can calculate the temperatures if somebody can help thanks. & does anyone has this book that have this graphs?

    Thanks guys.

    Mahmoud

  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Condenser water inlet & outlet temperature

    Total Heat of Rejection Kws = flow rate Litres per second x 4.2 Kj/kg x TD' K

    TD' K = THR Kw / Litres per second x 4.2 Kj/kg

    generally water temp rise is 5.5' C or 10' F
    Last edited by Magoo; 18-10-2014 at 11:37 PM. Reason: edit