Results 1 to 3 of 3
-
15-10-2014, 05:31 PM #1
2xdaikin twin splits on 1 controller
Hi guys
I'm after running 2 x daikin twin splits off 1 controller indoor model numbers = FXFQ100AVEB
Is it a case of daisy chaining the p1 & p2 thru all 4 indoors and then to the controller ?
Or do you just daisy chain 2 master units and then to the controller
Many thanks
Colin
-
15-10-2014, 08:32 PM #2
Re: 2xdaikin twin splits on 1 controller
n.p on the controller to the 1st unit, then daisy chain n,p to the other unit. if its a twin split- 4 indoors, 2 condensers then you run the controller to 1 unit on 1 system then to the next unit on the other system, as your interconnect is looped thru both indoors on the same system
Last edited by install monkey; 15-10-2014 at 08:35 PM. Reason: saw you mention 4 indoors !
-
11-11-2014, 07:48 PM #3
Re: 2xdaikin twin splits on 1 controller
Cheers for that ... All sorted
I'm only really starting using Daikin as last 10 years I would say 90% of our installation has been Mitsubishi electric , so it's not quite comming second nature as it has done in the past