    Hi guys

    I'm after running 2 x daikin twin splits off 1 controller indoor model numbers = FXFQ100AVEB

    Is it a case of daisy chaining the p1 & p2 thru all 4 indoors and then to the controller ?

    Or do you just daisy chain 2 master units and then to the controller

    Many thanks

    Colin



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: 2xdaikin twin splits on 1 controller

    n.p on the controller to the 1st unit, then daisy chain n,p to the other unit. if its a twin split- 4 indoors, 2 condensers then you run the controller to 1 unit on 1 system then to the next unit on the other system, as your interconnect is looped thru both indoors on the same system
    Last edited by install monkey; 15-10-2014 at 08:35 PM. Reason: saw you mention 4 indoors !

  3. #3
    Join Date
    Nov 2013
    Location
    England
    Age
    42
    Posts
    33
    Rep Power
    0

    Re: 2xdaikin twin splits on 1 controller

    Cheers for that ... All sorted

    I'm only really starting using Daikin as last 10 years I would say 90% of our installation has been Mitsubishi electric , so it's not quite comming second nature as it has done in the past