Results 1 to 13 of 13
    Oct 2014
    Braga
    27
    3
    R290 as replacement of R404a
    Hi all!
    If I want to change the refrigerant (R404a to R290) of the equipment I need to do some changes like the compressor?
    Split Croatia
    52
    6,108
    30
    Re: R290 as replacement of R404a
    Yes! Compressor Oil, expansion device etc... Depending on system.
    May 2012
    54
    1,328
    30
    I'd be more worried about the electrics.
    Some R290 systems I've seen use standard R404a compressors
    and TEV's but the electrics are different.
    Make sure all the electrics are either sealed or up or out of the way of
    any possible refrigerant leaks. All fan motors need to be constructed
    to a certain standard.
    EX rated motors
    (see http://www.hse.gov.uk/offshore/infosheets/is3-2010.htm for brief description).
    Fortunately most fridge motors are of an EX construction.
    Compressor starting and defrost control is the area that needs most attention.
    Anywhere on the system where a spark can take place (HP & LP switches) need
    to be sealed or removed up and out of the way.
    Rob
    May 2012
    54
    1,328
    30
    In the UK we don't recommend retro fitting an existing fridge to R290.
    It can be done but full risk assessments need to be taken beforehand.
    Rob
    Oct 2014
    Braga
    27
    3
    Thanks guys,
    And what you think about performance? It will be better for same custs?
    May 2012
    54
    1,328
    30
    Quote Originally Posted by tiagomartins007 View Post
    Thanks guys,
    On paper it should be more efficient.
    In real life with all the variations that there are, you might
    find it to be no better or no worse.
    Rob
    Apr 2006
    35
    1,646
    I find on real world usages for air conditioning systems it proves to be much better in performance for cooling Vs electrical consumption., keeping in mind these are smaller systems.
    Now in Redvers Sask.
    Oct 2014
    Braga
    27
    3
    And what about legislation?
    I read this
    "IEC 60335-2-24 and IEC 60335-2-89 currently restrict the charge size for commercial refrigerators
    and freezers and household refrigerators and freezers to 150 g of flammable refrigerant, respectively.
    This charge amount is considered to be safe if the appliance itself is tested for safety. The standard
    does not establish safety guidelines for units with a propane charge greater than 150 g"
    It meens it cannot be comercialized??
    May 2012
    54
    1,328
    30
    Your location says Braga. Braga in Portugal?
    You are European same as me and we use the same legislation.
    Depends on what you want it for.
    150 g is the limit for mobile and integral systems
    1.5 Kg is the limit in public areas (can go upto 5 Kg)
    2.5 Kg is the limit in commercial - private areas (can go upto 10 Kg)
    10 Kg is the limit for commercial - industrial areas (can go upto 25 Kg)
    No limit for a self contained packaged unit in a secure well ventilated area.
    This is a European directive so should be the same throughout Europe,
    but you will need to do training and research your local rules and regulations.
    Rob
    Jun 2010
    Yorkshire
    520
    14
    From what I remember when doing my first f gas certificate, the 2078, we just covered the storage and transportation of it, 3kg rings a bell when being used/stored in a room of 10 cubic meters. Only once ever come across it once and that was back in the early eighties on an old Carlisle water chiller centralised unit specifically made to run on lpg, that we decommissioned. Infact that was the first time that we ever used a recovery unit, that in turn was built by my boss out of canabalised parts, it took all day to fill 3x 30lb dumpies.
    And all the time being supervised by a clark of works that possesed no instruction or method statement, only ever asking us about our method of decommissioning then just simply agreeing with us and giving us permission to go ahead and refrain from smoking and using sources of ignition.
    Non of us could understand why this gas was being used, as we only ever come across r12 and r22 back in those days, and once came across a gas that was ether based, and we didn't know it had that inside until venting it. And it was me that found out it was ether as I ended up passing out whilst up the ladder. We just put it down that some boffins must have built it who knew about that kind of thing back then.
    I myself don't posses the lpg based licence but do however have the category on my gas safe card to work with it as a fuel. And I should imagine that low level ventilation would be a requirement when being used/stored inside a building? And as other posts state, the controls would have to be either intrinsically safe or class 2 flame proof category as a minimum, or standard controls located within a prescribed zone?
    Training may be finished but experience is never complete.
    Feb 2010
    GREECE
    43
    33
    Well ... why not go for the R407A??? instead?
    It will be a straight forward change with less hassle ...
    Now in case want for research... R290 requires changing the Condenser as well..
    For replacing the quantity of refrigerant... A very easy apply is that R290 will be the 1/3 of nominal R404A refrigerant supply. therefore Charge with 1/3 of the nominal capacity as the tech sticker suggest...
    Of course you may need to reduce or increase charging by grams...
    Feb 2015
    uk
    36
    having had a lucky escape from a call out i went to were cowboys had filled a r134a system with r290 without telling anyone or even labeling the unit up as a flammable gas i would say stick with r404a as long as possible because when that stuff goes up it really goes up
    2,609
    29
    Quote Originally Posted by abp32 View Post
    Because of the "Cowboy" problem, we have a procedure & equipment to check systems before working on them, to check refrigerant is not propane etc.
    This is used on equipment we have not worked on or have history.
    You may only get one chance to check it or get it wrong, before accident happens.