    please i need your help i want to find the p-h& t-s chart for R502 and what is this type of ***** the SUVA HP62?
  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    68
    Posts
    3,362
    Rep Power
    32
    Re: p-h &t-s chart
    Hi.
    google your requests , plus DuPont refrigerants.
  3. #3
    Join Date
    Sep 2010
    Location
    yemen
    Posts
    16
    Rep Power
    0
    Re: p-h &t-s chart
    Hi
    thanks very much
  4. #4
    Join Date
    Oct 2007
    Location
    sweden
    Posts
    93
    Rep Power
    14
    Re: p-h &t-s chart
    Why R502??
    Saturation value table for R502, p-h and t-s chart can you make itself if you using 'coolpack' software package, under refrigeration utilities (program is free, and coming from Danfoss)
    but...
    R502, R22, R12 and other blend with CFC-refrigerant is forbidden in many year in EU-country, now forbids also R404A, 407C, 410A, R134a, R143a, R125 etc. in EU depend of high GWP-value.
    I hope you only want information about R502 only for comparison - not for new design.
    all above refrigerant is now dead refrigerant - have no future
    If you design new equipment, choice of allowed refrigerant in EU is now:
    blend of R290/R600a, pure R1270, R290, RR600a, DME (R-E170), blend of R1270/R170 (for simulate R410A pressure range), R32 (flammable, give very high head temperature in one stage compression, not direct replacement for R410A...), HFO1234yf (for replace R134a and now questioned in car using), R152 (for replace R134a, also flammable), ammonia and few more.
    all refrigerant above 750 GWP going to be forbidden in EU.
    Depend of GWP is lower than 750 mostly of usable refrigerant is more or less flammable and some of them make strong and life treating poison in fumes in case of burning (R152a, HFO1234yf, R32 - and why HFO1234yf is questioned in car using)
    New designed equipment need designed to handle flammable refrigerant on safe way