    I need help. please. can't figure out what's wrong



    Hi. I'm new here but been reading stuff here for long time.
    I have a farmers market and we have a 24 ft display open cooler. We recently had to change the compressor because old one has died. And ever since then it's been working like a champ(it's been 3 months now). But just few days ago. End part of our cooler stopped working like it should. Display case is 2 X 12 ft connected together and has 2 side for each case. Everything works good except the one end side started not working. All side used to keep at 5 degrees to 14 degrees but since few days ago. That one side has been keeping at 14 degrees when it's in and 20 when it's off. So it's as same as if not working at all. I thought it was frozen somewhere but it's not the case. Please give me your thoughts.



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: I need help. please. can't figure out what's wrong

    Shortage of gas get the guy back who changed the compressor,hope he changed the filters!

  3. #3
    Join Date
    Aug 2013
    Location
    horsham
    Age
    37
    Posts
    28
    Rep Power
    0

    Re: I need help. please. can't figure out what's wrong

    Are you sure all the Evap fans are running if fitted?

  4. #4
    Join Date
    Oct 2014
    Location
    america
    Age
    42
    Posts
    3
    Rep Power
    0

    Re: I need help. please. can't figure out what's wrong

    Quote Originally Posted by tonashp View Post
    Are you sure all the Evap fans are running if fitted?
    Yes. They r spinning blowing warm air. ..

  5. #5
    Join Date
    Oct 2014
    Location
    america
    Age
    42
    Posts
    3
    Rep Power
    0

    Re: I need help. please. can't figure out what's wrong

    [QUOTE=cadwaladr;301435]Shortage of gas get the guy back who changed the compressor,hope he changed the filters![/QUOTE
    Do you think I might have a ***** leak ?
    And when u said filter.. what kind of filter for what would you be referring to? Thank you for your reply sir btw.

  6. #6
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: I need help. please. can't figure out what's wrong

    The liquid line filter it will have one of some description,did the engineer do a nitrogen pressure test and vac it out when he changed the faulty compressor,finally what caused the old one to fail? as that may be the cause of the problem you have now.

  7. #7
    Join Date
    Aug 2013
    Location
    horsham
    Age
    37
    Posts
    28
    Rep Power
    0

    Re: I need help. please. can't figure out what's wrong

    Sounds like a leak of refrigerant (*****), a pressure leak test and good vac should be carried out after opening the system. If it won't hold pressure it shouldn't be recharged without finding and repairing the leak.

    Is the compressor running?