Results 1 to 7 of 7
  1. #1
    Join Date
    Oct 2014
    Location
    UAE
    Posts
    4
    Rep Power
    0

    30XA0502----0249-PEE- Carrier air cooled chiller



    Dear Sir,
    i am facing High oil filter drop pressure, Oil pressure transducer, Economizer pressure transducer and water exchange temprature sensor swapped alarms in 30XA0502----0249-PEE- Carrier air cooled chiller.
    What to do?
    How many gallons oil required for MODEL NUMBER:06TSA186SJ1C ( Carlyle) compressor
    Last edited by arulzr; 11-10-2014 at 08:59 AM.



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: 30XA0502----0249-PEE- Carrier air cooled chiller

    welcome to re. first make it clear , what is the alarm code?

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: 30XA0502----0249-PEE- Carrier air cooled chiller

    http://dms.hvacpartners.com/docs/100...0f/30xa-1t.pdf
    manual for chiller
    page 61 for what type of oil, and how to top up- might be worth checking oil solonoid is open and oil filter isnt blocked/restricted

  4. #4
    Join Date
    Oct 2014
    Location
    UAE
    Posts
    4
    Rep Power
    0

    Re: 30XA0502----0249-PEE- Carrier air cooled chiller

    As shown in the Touch pilot display the following four alarms are showing,
    1.Circuit-A High oil filter drop pressure.
    2.Oil pressure transducer.
    3.Economizer pressure transducer.
    4.Water Exchanger temprature sensors swapped.
    And also i found small leakage in the plug fuse which is located in Economizer pipe line back to compressor.

  5. #5
    Join Date
    Oct 2014
    Location
    UAE
    Posts
    4
    Rep Power
    0

    Re: 30XA0502----0249-PEE- Carrier air cooled chiller

    Dear Sir,
    As shown in the Touch pilot display the following four alarms are showing,
    1.Circuit-A High oil filter drop pressure.
    2.Oil pressure transducer.
    3.Economizer pressure transducer.
    4.Water Exchanger temprature sensors swapped.
    And also i found small leakage in the plug fuse which is located in Economizer pipe line back to compressor.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: 30XA0502----0249-PEE- Carrier air cooled chiller

    dear sir- please look at post 3, the 1st line is highlighted- its a link to the service manual
    click where it says "http://dms.hvacpartners.com/docs/100...0f/30xa-1t.pdf"

  7. #7
    Join Date
    Oct 2014
    Location
    UAE
    Posts
    4
    Rep Power
    0

    Re: 30XA0502----0249-PEE- Carrier air cooled chiller

    Dear Sir - Thank you very much.