    Unhappy TK V500 semi-hermetic compressor insulation test varied results



    Hi all. Went to a job other day and customer was complaining
    About no standby operation. (240v single phase) Checked the source and found mains power
    Had been tripped. Meggered the extension lead, tested all ok.
    Reset the mains, unit started but cut out very quickly.
    Reset mains once again, this time manually pushing the contactor in
    with the same result once again cutting out immediately.

    Isolated all wiring from windings and found windings going straight to
    Ground @ 500V test.

    Strangest thing though, I have since removed the compressor and drained the oil
    Only to retest the windings on a bench and @ 500 V resistance is infinite!
    Has anyone else seen anything like this before?!



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: TK V500 semi-hermetic compressor insulation test varied results

    Put the oil back in,then test again

  3. #3
    Join Date
    Oct 2014
    Location
    Australia
    Posts
    37
    Rep Power
    0

    Re: TK V500 semi-hermetic compressor insulation test varied results

    Really? What if it tests ok then?!!?

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: TK V500 semi-hermetic compressor insulation test varied results

    Quote Originally Posted by swampy84 View Post
    Really? What if it tests ok then?!!?
    Damp motor winding which may of dried out since the first test, COULD? be the cause?
    Moisture in a stored motor will give similar results.
    Strange given what you have done all the same!
    Swampy has a good point if using synthetic oil within this comp.
    The oil has the ability to become highly saturated with water if not stored or used correctly.
    Grizzly

  5. #5
    Join Date
    Oct 2014
    Location
    Australia
    Posts
    37
    Rep Power
    0

    Re: TK V500 semi-hermetic compressor insulation test varied results

    Good point, never really thought of that really. In which case if the windings have gone to ground due to poor oil condition... The oil used is polyol ester oil. So yeah very hygroscopic.....

  6. #6
    Join Date
    Oct 2014
    Location
    Australia
    Posts
    37
    Rep Power
    0

    Re: TK V500 semi-hermetic compressor insulation test varied results

    I guess that long story short is I don't want to put this motor back in
    That may only last a few months as it's in a prick of a spot.
    Mind you I don't want to replace if It's not necessary either.
    Surely if the oil has gathered so much moisture and or has turned acidic
    The windings wouldn't be in the best condition

  7. #7
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: TK V500 semi-hermetic compressor insulation test varied results

    If in doubt sling it out!

  8. #8
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: TK V500 semi-hermetic compressor insulation test varied results

    I used to get problems with early ones the terminal box on the compressor was prone to letting water in ,I used to put a small sheet of ally on the grill/cover it was worse if it snowed.