    1- i have a condenser water pump of 102 L/s how much is the size of the pump? which catalogue i can find the selection for the pump.
    2- the flow rate for the condenser water pumps is it based on 3usgpm/ton?

    Thanks,,



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: condenser water pumps

    Try one of the major pump manufacturers.

    Lots of variables involved, duty, pressure, voltage, power consumption.

    One choice - Grundfos Pumps

    http://uk.grundfos.com/grundfos-isol...ler-unit1.html
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: condenser water pumps

    Hi mah_h
    as per Brian UK , there is a lot involved with selection of water pumps. Engage the services of a pump supplier that can analyse your application., then supply the correct pump or pumps.

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: condenser water pumps

    when you are choosing pump you rate better be in the medial of rang pump can work.
    In condenser pump you need circulation pump and meanly 1450 RPM.
    your inlet size for piping should be one size bigger than outlet size.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: condenser water pumps

    1 US Gallon = 3.8 Litres
    3 US Gal/m/Ton = 3.8x3/60 =0.19 l/s/ton

    102l/s / 0.19 = 631Ton of refrigeration = 2221kW

    You will need a big pump

  6. #6
    Join Date
    Oct 2014
    Location
    dubai
    Posts
    8
    Rep Power
    0

    Re: condenser water pumps

    Thanks Brian

  7. #7
    Join Date
    Oct 2014
    Location
    dubai
    Posts
    8
    Rep Power
    0

    Re: condenser water pumps

    Quote Originally Posted by Magoo View Post
    Hi mah_h
    as per Brian UK , there is a lot involved with selection of water pumps. Engage the services of a pump supplier that can analyse your application., then supply the correct pump or pumps.
    Thanks Magoo

  8. #8
    Join Date
    Oct 2014
    Location
    dubai
    Posts
    8
    Rep Power
    0

    Re: condenser water pumps

    Quote Originally Posted by frank View Post
    1 US Gallon = 3.8 Litres
    3 US Gal/m/Ton = 3.8x3/60 =0.19 l/s/ton

    102l/s / 0.19 = 631Ton of refrigeration = 2221kW

    You will need a big pump
    Thats right. Thanks Frank.