    Apr 2012
    Australia
    33
    Screw compressor resonance/vibration in discharge
    Long time reader, first time caller
    My company did a DX plant upgrade (A/C) and have installed a 134a bitzer screw (around 300kw capacity) which was sized and designed by a separate engineer. The discharge pipework has a very loud internal resonance coming from 2 spots (*): brief pipe rundown
    Rises from compressor then horizontal 2m
    *a straight that drops and climbs with two 45 degree bends with 1m in between elbows
    5m then right bend then 15m
    *a left hand bend, runs 1m drops vertical 0.5m then straightens horizontal (loudest)
    Then outside to condenser
    The unit is still slightly undercharged going off vessel on pump down (DX so unsure of full), the discharge pipe work is 2" 1/8, no mufflers/eliminators
    Addition of gas towards 'full' has helped and reduced pulsations a little
    All fixings are tight but not really relevant given the nature of the noise
    Pressures run around 780-800kpa (pressure controlled) and 210 kpa
    Neither myself or my supervisor have had much experience with this issue, can anyone provide insight into what's causing the noise? And/or a solution?
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    Re: Screw compressor resonance/vibration in discharge
    better post a picture of the pipe work of discharge line
    manchester
    5,639
    is it when the compressor stops or during running?
    70
    4,700
    47
    Pulsing within the discharge line can be a result of the system being undercharged particularly when you have no liquid seal within the receiver.
    Check the temp of the liquid line?
    Screws also have a natural resonance at certain running conditions.
    Sadly you may have to call in someone if you feel its a issue.
    Sorry to be vague.
    Apr 2012
    Australia
    33
    Thanks for the quick responses guys.
    I'll get a picture when I go back next, maybe even a video of the noise.
    During normal running
    I'm assuming the receiver would have a pickup at the bottom on the outlet but looking at it makes me think it's just on the side, but sight glass is always full now, it was a little short on liquid before, receiver has 3 sight glasses and all were empty but bottom one stays full now after addition of gas. Haven't got a number for the liquid line only feel which was deemed okay.
    Were going to talk to the guy who designed it because ultimately if he designs them he should have come across this before
    3,362
    Quote Originally Posted by Rexy View Post
    There has to be an oil seperator in there somewhere as well!
    Apr 2012
    Australia
    33
    Nope no seperator, it's a drop in compressor unit so I guess whoever designed it decided it dosent need it.
    Pictures go from outside back to plantroom
    We're going with a discharge muffler either on the rise out of the compressor or on the first horizontal
    The systems designer couldn't confirm if it'll fix it or not but we don't have many options
    Jun 2011
    Australia
    44
    336
    Would you have a picture of the package / compressor?
    Apr 2012
    Australia
    33
    Attachment 11797
    Old and bad angle but all I have for the moment
    Apr 2012
    Australia
    33
    And the discharge muffler has fixed it
    Jun 2011
    Australia
    44
    336
    Thanks, always good to know the outcome - cheers!