    R12 12 volt Danfoss Compressor to R134a



    Hello,

    I hope you clever folks could help me out.

    I have changed a very old R12, 12 Volt compressor on a very small narrow boat fridge for an R134a 12 volt.

    The Small Ice Box Refrigerator is hand made, was originally built using a 20 odd year old LEC ice box evaporator. There was no refrigerant charge on the hand stamped plate.

    So, I replaced the compressor and have charged it with R134a to around 0 (Zero) Psi. Ran for 2 hours with no ice on the suction, just slight sweat.

    The client has been back on to say the appliance cools but runs 100% of the time, draining his limited battery bank (Ah's unknown to me at the moment).

    A mate of mine has suggested that I change the refrigerant to R49 !? With a charge of 10% less than that of the original (unknown of course).

    I was thinking maybe R600a instead?

    I have used R600a in an R134a job before. But not sure about the compatibility of R49 in R134a compressors.

    Any help, suggestions or advice would be greatly appreciated please?.

    TM



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: R12 12 volt Danfoss Compressor to R134a

    .

    Keep with the R134a for now, it is just a little bit under charged.

    A fridge in case temp of about +5 will have an evap temp of about -5,
    the pressure of 134a at -5 is about 1.4 bar ( 20psi).

    You need to have a back pressure of about 1 and a bit bar for it to
    have enough refrigerant. If it freezes back down the suction you have
    put a bit too much in.

    Rob

    .
    Last edited by Rob White; 09-10-2014 at 12:39 PM.
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Oct 2007
    Location
    Manchester
    Posts
    15
    Rep Power
    0

    Re: R12 12 volt Danfoss Compressor to R134a

    Thank you Rob.

    I was taught an Evap Temperature difference should be around 10 to15c?

    TM

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: R12 12 volt Danfoss Compressor to R134a

    Quote Originally Posted by teemyob View Post
    Thank you Rob.

    I was taught an Evap Temperature difference should be around 10 to15c?

    TM
    Evap temps are very general and can vary.

    Most often, most engineers work to approx 10 degs diff.

    Some sytems can be as low as 3 and some as high as 15 degs
    but for most evaps it's about 10 (ish)

    regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: R12 12 volt Danfoss Compressor to R134a

    .

    I did a job on a 12 volt fridge in a canal boat once,
    lovely little thing and in a very picturesque setting.

    It's a shame the owner tried to defrost the thing with a knife
    The evap had more holes in it than a Swiss cheese.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  6. #6
    Join Date
    Oct 2007
    Location
    Manchester
    Posts
    15
    Rep Power
    0

    Re: R12 12 volt Danfoss Compressor to R134a

    Thanks again, I will go back and charge again to around 10 psi(g)?

  7. #7
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: R12 12 volt Danfoss Compressor to R134a

    Don't forget: The Danfoss BD 2.5 used mineral oil with R12. With R134a, you should be using synthetic oil.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.