Results 1 to 10 of 10
    Dec 2011
    Saudi Arabia
    8
    Gree Aircon GWH12MB-D1NTA3A/1
    Sir, My Boss Just only call me that his aircon Gree Gwh12mb-d1nta3a/1 is not cooling the technician said that when he ON the unit then he set it to cool mode his pressure gauge was damaged because the pressure is high. Then he used the high side of the gauge he connect it to the suction port or low side port and he reads the pressure is almost 400 psi and the suction port is hot also when he touch it. He OFF the unit then try to ON again the compressor did not work only the outdoor fan the internal overload opens that was he said and the amperage in the unit is 8.9A or 9A only but the amp meter reads 11amps. What maybe the problem of this unit pls help so when I go there it not hard to me check Thank u very Much
    Dec 2011
    Saudi Arabia
    8
    Re: Gree Aircon GWH12MB-D1NTA3A/1
    And I ask my Boss if the Technician check the fault or error codes the technician didnt check it.
    Split Croatia
    57
    6,151
    36
    If he really changed mode to cooling before connecting gages, than 4 way valve is stuck at heating position. If this is right after installation, than wiring between indoor and outdoor unit is mismatched.
    If actual mode is heating, than pressure is normal.
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2008
    u.a.e
    49
    412
    23
    better to to replace the 4 way valve. its internal mechanism has damaged.
    Dec 2011
    Saudi Arabia
    8
    Thank u very much sir for the help!!
    Dec 2011
    Saudi Arabia
    8
    Thank U vry Much sir for the reply it will help me a lot thank u to both of you
    Apr 2012
    Iraq
    35
    623
    as the members above he might be incorrectly wired indoor to outdoor
    or the 4 way valve (reversing valve is stuck)
    if the ac is new
    return it under warranty
    im familiar with GREE ac
    they are high quality ac
    Power consists not in being able to strike another but in being able to control oneself when anger arises
    Dec 2011
    Saudi Arabia
    8
    thank u sir I went there yesterday I replaced the 4 way valve I test the old one discharge to evaporator is open even it not energized. The solenoid is working the but mechanical inside the valve was defective. I test also the compressor because I dont know how many days or hours the unit is working with defective 4 way valve. Maybe tomorrow saturday I will vacuum the system coz it midnight already when I finish. Thank u sir for the reply.
    Dec 2011
    Saudi Arabia
    8
    Thank U very much to nike123, moideen, and kefah to all your reply It helps me a lot. I think it also the 4 way valve but I need some Idea from EXPERTS thank u very much. Gud Luck
    Apr 2012
    Iraq
    35
    623
    the 4 way valve could be factory faulty if it was new
    u have just to replace it
    check it with nitrogen for leaks
    make god vacuum then charge the system by weight