    c room ices up



    Hi guys got a coldroom r404a the unit ices up every 2 weeks its elec df all gas prssures are ok but i checked all perameters
    Df stop temp 20
    Fans active no
    Def duration 20
    Def cycles every 4 hours
    Fan start temp 0
    Its a single heater evap which works well have i missed anything when checking it over also the drain is clear any help is appreciated



  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: c room ices up

    Hi Matt,

    Does the defrost probe read correct?
    Defrost heater getting hot?

    Yeah, the obvious bits I guess you've checked but this caught me out once:

    Defrost heater come unclipped on the bottom of the coil (Rivacold blower). Coil heated up a bit, enough to get probe hot but back of coil not clearing, just melting a bit so a week later iced back up.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  3. #3
    Join Date
    Jan 2012
    Location
    West midlands
    Age
    44
    Posts
    33
    Rep Power
    0

    Re: c room ices up

    Hi,

    Sounds like the is door being left open. Is their a door switch or curtain?
    If not that I would second the defrost probe faulty or located to close to the heater bar.
    After that is the controller relay stopping at temp or solenoid passing.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: c room ices up

    Hi Matt.
    Has the products that are being stored recently changed?
    Only some seasonal products have High moisture contents.
    Has the frequency of the through-put changed.
    Even more basic Has the drain line vapour seal or the door threshold seals been damaged
    Someone may have to pay for you to spend some time with this one. The answer will be their somewhere?
    Have you got lazy staff that leave the door ajar whilst they load to and from the store.
    Stupid it may be but the above can happen.
    Sorry coolhand I have just read your post.
    Great minds eh!
    Grizzly

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: c room ices up

    if its a walk in freezer- increase the defrost duration - to say 30 mins, just in case its not clearing all the ice, as others say check the door closes properly and the seal is compressed, also any air balance vent not closing?

    had issues with a searle freezer a few mth ago- like an icy wonderland in there- blocked drain , replaced it all in 32mm plastic , no issues since ( watch me get a call out to it now!)

  6. #6
    Join Date
    Mar 2011
    Location
    england
    Age
    34
    Posts
    101
    Rep Power
    14

    Re: c room ices up

    Well i read all your posts and i know the seal is good the door os alsp self closing the drain is clear the only thing i am assuming at the minute is the chefs put cardboard boxes directly under the fans restricting the air flow

  7. #7
    Join Date
    Aug 2013
    Location
    horsham
    Age
    37
    Posts
    28
    Rep Power
    0

    Re: c room ices up

    Increase the duration to 45mins. I have had similar probs with a zanotti, end temp set to +5. Make sure the probe reads good and is at the top of the coil as far from the heater on the inside of the blower if possible.
    What type of blower is it?

  8. #8
    R ALLATT's Avatar
    R ALLATT Guest

    Re: c room ices up

    What make and type of evaporator do you have

  9. #9
    Join Date
    Mar 2011
    Location
    england
    Age
    34
    Posts
    101
    Rep Power
    14

    Re: c room ices up

    I think its a luve evap

  10. #10
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: c room ices up

    Is it snow or ice on the evap.
    Is there a drain down parameter if so set to 5mins.
    Put through a defrost and check if there is any ice still on the evap. if there is move termination sensor to this position.

  11. #11
    R ALLATT's Avatar
    R ALLATT Guest

    Re: c room ices up

    I would check you have the right speed evap fan motors fitted.
    Fully defrost the coil put on defrost and if the controller lets you, watch what temperature the defrost probe terminates the defrost.

  12. #12
    Join Date
    Sep 2013
    Location
    uk
    Posts
    6
    Rep Power
    0

    Re: c room ices up

    hi, could possibly be the liquid line solenoid valve passing .
    also if an electronic controller is being used check the compressor relay isnt sticking ,seen this many times

  13. #13
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: c room ices up

    where is the position of Evap. in room . it is important .

  14. #14
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Re: c room ices up

    1 fan freezer iced up.jpg like this

    or fluffy ice on back face

    iced up.jpg
    Last edited by Toolman; 11-10-2014 at 12:08 AM.
    60% of the time it works everytime.

  15. #15
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Re: c room ices up

    Quote Originally Posted by mattym View Post
    Hi guys got a coldroom r404a the unit ices up every 2 weeks its elec df all gas prssures are ok but i checked all perameters
    Df stop temp 20
    Fans active no
    Def duration 20
    Def cycles every 4 hours
    Fan start temp 0
    Its a single heater evap which works well have i missed anything when checking it over also the drain is clear any help is appreciated
    Some answers above are for freezer system ice ups.

    But you say its a coolroom ? Sounds like a freezer setup , heaters and fans active =no

    The back pressure ( LP ) must be low for it to ice up if a coolroom ?

    If its not LOW then make controller work on time only not temp termination.
    60% of the time it works everytime.