    chiller shutdown due rapidly decreasing of cooling temp.
    Hi
    I got a Trane water cooled screw tripped due a rapidly decreasing of condenser enter. water temperature. The entering water temp. slowed down too fast ( from 44 oC to 30oC) in a minute when the chiller was running so chiller controller automatic shut down, i have not see any error message on control panel. so what's reason for this shutdown ? and have anything to check to prevent failure ?
    Anyone knwo please help me
    Regards
  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19
    Re: chiller shutdown due rapidly decreasing of cooling temp.
    hi wta 12,
    are you sure that is the condenser not the evaporator temp?= sedgy
  3. #3
    Join Date
    Aug 2011
    Location
    vietnam
    Posts
    39
    Rep Power
    0
    Quote Originally Posted by sedgy View Post
    hi wta 12,
    It's exactly condenser temp. they suddenly slowed down due we have no condenser fan control (running 100 %)