    Small slit nitrogen wiv braze



    1. Standard nitrogen cylinder is heavy and unwieldy to use while brazing small splits. Gauges need constant readjustment for the minisicule flow required..

    We are looking at using an old r22 dumpy 9kg bottle with a bespoke small regulator designed for very low flow. Anyone else tried this? Anyone found a quick easy way to get very low flow needing little adjustment ?
    What pressure did you fill r22 dumpy to for max duration?
    Anyone come across a quick way to connect to ¼ 3/8 ½ 5/8 copper as required?

    2. Sometimes there are only two brazes on a single split installation and these real difficult to set up. Its tempting not to use nitrogen, however having had a modern electronic refridgerent flow valve apart it looks as though even the smallest contaminant could cause a problem. There are inline gauze filters on these. Your opinions valued folks…. (leave out the warranty issue, we are looking at the level of risk for malfunction over life of unit on a difficult setup with limited number brazes on the odd occcasion..as allways one callback or malfunction completely negates saving couple hours time…)



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Small slit nitrogen wiv braze

    .

    There are two parts to this, the practical bit and then the sensible bit.

    I'll do the practical bit first.

    Just do the maths.

    A small OFN cylinder is charged at 200 bar, you have a
    small dumpy and it's max pressure would be less than 30 bar.

    If you filled it to 20 bar for safety sake.

    If the cylinder is 10 Kg, that's about 10 litres, 10 ltr X 20 bar
    is about 200 ltr. Your flow rate should be at 1 bar - 2 ltr a minute.

    200/2 = 100 mins, allowing for losses and and irregularities that could
    be reduced to 60 mins.

    60 mins is a reasonable amount of time and should be long enough for a
    small split.

    Now the sensible bit.

    Do not under any circumstances use a cylinder for something it is not designed for.
    Do not under any circumstance adapt or adjust a regulator or valve and never use
    them for something that they are not designed for..

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Small slit nitrogen wiv braze

    The nitrogen bottles are like that for a reason.
    Irrespective of size they have to be able to withstand something like 3000 psi of standing charge.
    If you decant into another cylinder, you could inadvertently pressurise that cylinder to those sort of pressures.

    Don't go there the chances of this going wrong well outway the inconvenience of using the proper kit.
    There are small manageable cylinders out there just check out the suppliers.
    Besides which it's a bad option you are considering with all the liability on whoever does it!
    Grizzly

  4. #4
    Join Date
    Jul 2009
    Location
    london
    Posts
    69
    Rep Power
    15

    Re: Small slit nitrogen wiv braze

    Thank you for first reply, absolutely helpful, we were looking at around 200psi and vey useful calculation of volume available.
    and for second reply... did not know one could obtain tiny nitrogen cylinders and is now being ordered so no need struggle with a dumpy.

    nb. decanting into dumpy r22 cylinder wouldnt have been a problem using nitro regulator set at 200psi (hundred) and aircon guages, and as first reply could have been a viable option. thank you.

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Small slit nitrogen wiv braze

    nb. decanting into dumpy r22 cylinder wouldnt have been a problem using nitro regulator set at 200psi (hundred) and aircon guages, and as first reply could have been a viable option. thank you.
    That's what I used to think as well, until it was explained to me how the regulators work and they can malfunction.
    Which is another reason for the advise given.
    Glad to assist!
    Good Luck.
    Grizzly.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Small slit nitrogen wiv braze

    Mostly found in Oxfordshire, UK :)

  7. #7
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Small slit nitrogen wiv braze

    There are some crazy people in our industry?

  8. #8
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: Small slit nitrogen wiv braze

    Yup, one of them likes farming and one big old silly looking diesel truck (and making videos)

  9. #9
    Join Date
    Sep 2008
    Location
    england
    Posts
    429
    Rep Power
    20

    Re: Small slit nitrogen wiv braze

    Use a flow meter combined with a two stage regulator. Manifold gauges are hopeless for controlling a very low flow:
    http://www.amazon.co.uk/Turbo-Torch-.../dp/B0076O41IK

    As they say on the BBC: other flow regulators are available

  10. #10
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Small slit nitrogen wiv braze

    Quote Originally Posted by glenn1340 View Post
    Use a flow meter combined with a two stage regulator. Manifold gauges are hopeless for controlling a very low flow:
    http://www.amazon.co.uk/Turbo-Torch-.../dp/B0076O41IK

    As they say on the BBC: other flow regulators are available
    And as Amazon Say "Currently Unavailable"!
    Grizzly