    Scotsman commercial H2O inlet valve



    I have an old Scotsman commercial ice maker- model CM250. The water inlet valve solenoid is constantly open, so the ice production is very slight.
    I want to be sure that the valve is defective before I get another one from Johnstone Supply, since it is over $30. Can I take it out and apply power to the valve from another source, to see if it opens and closes?
    Or should I put a voltmeter on the two wires going to the valve from the control box?
    Any help is appreciated.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Scotsman commercial H2O inlet valve

    If you think that the valve is always open then REMOVING power from the valve would enable you to see if it closes off the water supply.

    If it does stop then it would appear that you may have a control problem elsewhere.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2006
    Location
    pasadena, ca
    Posts
    6
    Rep Power
    0

    Re: Scotsman commercial H2O inlet valve

    Brian, thanks for the reply.

    removing the two wires that attach by spade plugs does not close the valve, the water continues to flow. I think that it is a bad valve.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Scotsman commercial H2O inlet valve

    If you have difficulty finding a Scotsman part try your local washing / dishwasher service depot. Most of the water valves are basically the same.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Apr 2006
    Location
    pasadena, ca
    Posts
    6
    Rep Power
    0

    Re: Scotsman commercial H2O inlet valve

    Brian, thanks for the info.

  6. #6
    Join Date
    Feb 2005
    Location
    Jamaica
    Posts
    121
    Rep Power
    20

    Re: Scotsman commercial H2O inlet valve

    Cannt the valve be cleaned? it might be just scale keeping the valve open,try cleaning if possible

  7. #7
    Join Date
    Apr 2006
    Location
    pasadena, ca
    Posts
    6
    Rep Power
    0

    Re: Scotsman commercial H2O inlet valve

    Quote Originally Posted by jamcool
    Cannt the valve be cleaned? it might be just scale keeping the valve open,try cleaning if possible
    Well, inspired by jamcool and Brian, and seeing how it is a slow Saturday in the restaurant, I removed the valve, cleaned it, put it back in, and this is how it is acting now:

    Water flows during the harvest cycle, as it should. At the end of the harvest, the water is supposed to stop flowing, but it does not. If I then turn off the water supply, the water stops (of course), and if I then turn on the water supply, the water does not flow through the valve until the next harvest cycle. But it won't stop on it's own.
    So the electronics seem to be OK, but the valve is not, correct?

  8. #8
    Join Date
    Apr 2006
    Location
    pasadena, ca
    Posts
    6
    Rep Power
    0

    Re: Scotsman commercial H2O inlet valve

    update - valve seems to be working now. Great! I'll check it after I come back after Easter Sunday.
    thanks to all.

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Scotsman commercial H2O inlet valve

    Sounds like the valve may be fitted wrong way round. The working fluid pressure normally keeps these valves shut and the coil raises the piston allowing the fluid to flow.

    When you cut off the water it closes but not when you de-energise the coil

  10. #10
    Join Date
    Apr 2006
    Location
    pasadena, ca
    Posts
    6
    Rep Power
    0

    Re: Scotsman commercial H2O inlet valve

    Just to follow up - I installed a new water inlet valve, actually a kit that applies to a few scotsman valves. first I installed it, and the water flowed like crazy. then I read the manual (RTFM), and put in the restrictor inlet that was for my machine. the water barely trickled out. I looked at the restrictor, and it had turned in the pipe, so I then straightened it out. Now the flow is perfect, the ice is building up, and I have a well functioning machine.
    Thanks for all the help.

Similar Threads

  1. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  2. 134a expansion valve question
    By g_norman in forum Technical Speculations
    Replies: 3
    Last Post: 18-03-2006, 03:06 AM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •