    hi guys, i need your help in understanding this topic... I'm working on a hotel (in Dubai) where all AHUs are being supplied at a supply temperature of 13.9 degree celsius then i got a comment from the hotel operator says:
    " cooling coils in all AHU's must be sized for full latent cooling for dehumidification and reheat coils are installed to raise the supply air temperature to the minimum design supply off coil temperature of 16 degrees celsius to ensure no cold drafts can be experienced anywhere in the hotel."
    supplying the temperature at 16 degrees it will increase the humidity in the space am i right?? is there any sub cooling to be done?
    thanks in advance
    Auckland
    68
    3,362
    32
    Re: Supply Temperature in an AHU
    Lowering air in cooling coil will increase RH%, then re-heat ( sensible heating ) will increase dry bulb and lower the RH%
    Oct 2014
    dubai
    8
    thanks.. in that case they need the supply temperature to be at 16 degrees where reheat coils are used when that pre function or ballroom isn't occupied(moisture content will be more) and then when that space is occupied we need to go to the sub cooling process back to provide a supply temperature of 13.9 am i correct?
    Auckland
    68
    3,362
    32
    Higher heat load from a function area ( humidity will be high ) so lowering off coil temperature will remove more saturation, adding sensible heat from re-heat coil will drop RH% even more and maintain a comfortable environment with a lot of people in function area. A higher percentage of fresh air is also required to maintain oxygen levels and stop the air becoming stuffy.
    Auckland
    68
    3,362
    32
    check site http://www.kwangu.com/work/psychometric.htm
    change any input and see changes in conditions.
    magoo
    Oct 2014
    dubai
    8
    thanks a lot my friend)) that was helpful
    Auckland
    68
    3,362
    32
    Hi mah_h