    Variable Amperage And Cold Liquid line



    Hi
    I have an A/c unit with scroll copmpressor.
    problem is: the liquid line specialy after sight glass is cold ( near of TXV is colder) and when compressor is started the amperage become High and variable.

    i read an article that said if there is a restriction, the amperage must be low because of starved Evap and low suction pressure.

    whats your idea?



  2. #2
    Join Date
    Apr 2010
    Location
    Qatar
    Age
    43
    Posts
    28
    Rep Power
    0

    Re: Variable Amperage And Cold Liquid line

    Replace filter drier

  3. #3
    Join Date
    Sep 2014
    Location
    Qom
    Posts
    10
    Rep Power
    0

    Re: Variable Amperage And Cold Liquid line

    i did but the problem is not solved

  4. #4
    Join Date
    Sep 2014
    Location
    Qom
    Posts
    10
    Rep Power
    0

    Re: Variable Amperage And Cold Liquid line

    unloaded compressor amperage is 13
    loaded is between 30-50 !!!
    seems there is a restriction such as oil in pipes
    do you agree?

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Variable Amperage And Cold Liquid line

    What is the compressor nameplate running amps?

    If it is running way above the nameplate FLC then it sounds like your compressor is goosed. A blockage will not make the compressor draw that sort of amps.

  6. #6
    Join Date
    Sep 2014
    Location
    Qom
    Posts
    10
    Rep Power
    0

    Re: Variable Amperage And Cold Liquid line

    copeland scroll ( nominal 30 A )

    so, you think Comp. is down.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Variable Amperage And Cold Liquid line

    Megger it to find out.

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Variable Amperage And Cold Liquid line

    Suction & discharge pressures at the same time would also be helpful.

  9. #9
    Join Date
    Sep 2014
    Location
    Qom
    Posts
    10
    Rep Power
    0

    Re: Variable Amperage And Cold Liquid line

    Discharge 225 psi
    Suction 45 psi
    Amperage between 35 - 50 ( copeland scroll / nominal 30 A)
    Unloaded: 13 A
    And the liquid line is cold specially after sight glass
    Last edited by hsn157134; 02-10-2014 at 09:50 AM.

  10. #10
    Join Date
    Feb 2014
    Location
    london
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: Variable Amperage And Cold Liquid line

    Was your indoor unit running as heat pump or cooling?
    Have you checked compressor winding?
    After sight glass should be warm subcooled liquid. If its cold that could be a sign short of refrigerant. If you refer to PH chart you will know the compressor will always pull too many amps when its under charged.

  11. #11
    Join Date
    Sep 2014
    Location
    Qom
    Posts
    10
    Rep Power
    0

    Re: Variable Amperage And Cold Liquid line

    its a cooling unit and the compressor winding is normal.
    there was problem when the charge was complete.
    plus, the sight glass indicator shows the system is wet.
    after a vacume, the problem was too.
    ( sorry for bad English)

  12. #12
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Variable Amperage And Cold Liquid line

    Measure the voltage going to the compressor when the compressor is loaded. Iranian supply should be 230 volts at 50 Hertz using single phase. (Source: Google search.)
    Are you using R22? Have you tested the Capacitors?
    The new filter/Drier will help sort the moisture problem but not the compressor.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  13. #13
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Variable Amperage And Cold Liquid line

    Drawing 30 Amps on any single electrical item at 240 Volts/ 50 HZ is beyond Australian standards. Drawing 30 amps on one phase of a 3 phase compressor is common in industrial applications.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  14. #14
    Join Date
    Sep 2014
    Location
    Qom
    Posts
    10
    Rep Power
    0

    Re: Variable Amperage And Cold Liquid line

    Its a 30 tones A/C with r22
    And I changed the drier but the problem is on.
    So I take the comp and sent for Seller to check it
    And I clean all of system.
    But I like to know whats the reason of problem.

  15. #15
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Variable Amperage And Cold Liquid line

    What voltage system is this thing operating on?

    (1) 30 Amp Scroll on a 30 Ton Chiller for (1) machine comes close to corresponding with a 460V 3 Ph 60 Hz arrangement....On 230 V 50 HZ the current should be a lot higher. What does the entire compressor nameplate read in terms of Voltages and Current?

  16. #16
    Join Date
    Sep 2014
    Location
    Qom
    Posts
    10
    Rep Power
    0

    Re: Variable Amperage And Cold Liquid line

    Quote Originally Posted by sterl View Post
    What voltage system is this thing operating on?

    (1) 30 Amp Scroll on a 30 Ton Chiller for (1) machine comes close to corresponding with a 460V 3 Ph 60 Hz arrangement....On 230 V 50 HZ the current should be a lot higher. What does the entire compressor nameplate read in terms of Voltages and Current?
    my mistake.
    15 tone is true and nameplate is 380V/ nominal A: 30