    Question Ecodan 14kw drawing 1.1A when off



    Hi all, hope someone can help,

    I have a 14kw mitsubishi ecodan heat pump (single phase) and while giving it a service I put a current clamp on it and found its drawing 1.11A when in mode 00. i.e off.

    This seems very high to me, anyone else experienced this or have any thoughts?



  2. #2
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: Ecodan 14kw drawing 1.1A when off

    crankcase heater ?

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Ecodan 14kw drawing 1.1A when off

    ~250W...

    Probably a bit too much to be controls or even a crankcase heater... A circulating pump?


  4. #4
    Join Date
    Sep 2014
    Location
    Uk
    Posts
    8
    Rep Power
    0

    Re: Ecodan 14kw drawing 1.1A when off

    When it goes into compressor warm up mode 08, it draws 1.3A and you can hear it, but when in mode 00 it is silent. i've been checking it every hour today and it is always 1.1A.

  5. #5
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,045
    Rep Power
    35

    Re: Ecodan 14kw drawing 1.1A when off

    Hi Simon,

    Came across this (on a Fujitsu split a few years back. Measuring with an amp clamp gave a high reading like yours when unit was at rest but if you used a power meter or whatever they are called - one that takes into account the power factor then actual current was very low.

    I'm no expert in power factors but it's something like if the current and voltage are in phase then power factor is one and perfect for an amp clamp. If it isn't then your amp clamp gives a false reading. AC units have a part of the PCB to improve the power factor which is where all this grief stems from.

    You can pick the meters up from Maplins or RS fairly cheap (search energy meters) or get stuck in and buy a posh one but it might pay to check this first before looking for a fault which might not be there.

    Incidentally your electric meter at home takes the power factor into account so don't panic there. As for how does current lead or lag the voltage, well don't think I'll ever get my head around that one.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Ecodan 14kw drawing 1.1A when off

    id be more concerned about the power consumption when its chuggin its nuts off

  7. #7
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: Ecodan 14kw drawing 1.1A when off

    Any beastie that sucks up that much power when off has something wrong with it. IIRC a crankcase heater would be maybe 50-60w, not 240w. And wouldn't power factor only account for a (perhaps) 20-30% measurement difference? The electronics of the inverter should help with that anyway.

    OTOH, maybe someone has been feeding it IM's frozen pizza crusts

  8. #8
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Ecodan 14kw drawing 1.1A when off

    Not familiar with these but on some inverter systems i think that rather than use a crankcase heater they partially power the windings to heat the compressor and sump up.Maybe this is the current your reading

  9. #9
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: Ecodan 14kw drawing 1.1A when off

    I agree with joe, and recall that the Ecodan occasionally powers up the compressor to maintain the oil temperature as it does not have a crankcase heater. I remember from the training course that it is recommended when installing the unit to connect up the power and turn it on with the interconnecting data cable disconnected to allow the windings to preheat the oil. I have never bothered to check the current being drawn by this process.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  10. #10
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Ecodan 14kw drawing 1.1A when off

    Joe is probably correct in his thinking . On Maneurop Invertor scrolls the Danfoss invertor gives a 24 volt dc supply through the motor windings to act as a crankcase heater . Thats probably why the current draw seems high ?.

  11. #11
    Join Date
    Sep 2014
    Location
    Uk
    Posts
    8
    Rep Power
    0

    Re: Ecodan 14kw drawing 1.1A when off

    It certainly sounds like it is powering the windings of the compressor to warm it it up, but when it has finished, and silent, it is still drawing power...and is still spinning my electrcity meter.

    I noticed a transformer on the main board is very hot all the time, could be the source i guess? But doesn't seem right.

    Simon

  12. #12
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Ecodan 14kw drawing 1.1A when off


  13. #13
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Ecodan 14kw drawing 1.1A when off

    Quote Originally Posted by Simon123 View Post
    When it goes into compressor warm up mode 08, it draws 1.3A and you can hear it, but when in mode 00 it is silent. i've been checking it every hour today and it is always 1.1A.
    so in mode 8 it pulls an extra 0.2amp -if its pulling 1.1 amp continuously, where are you taking this reading from? at the circuit breaker, outdoor unit,meter tails?

  14. #14
    Join Date
    Sep 2014
    Location
    Uk
    Posts
    8
    Rep Power
    0

    Re: Ecodan 14kw drawing 1.1A when off

    Quote Originally Posted by install monkey View Post
    so in mode 8 it pulls an extra 0.2amp -if its pulling 1.1 amp continuously, where are you taking this reading from? at the circuit breaker, outdoor unit,meter tails?
    I'm taking readings from the mains power cable where it connects to the screw terminals on the unit. I've also taken a reading at the meter tails and then switched the heatpump off at the isolator, and it dropped 1.1A

  15. #15
    Join Date
    Sep 2014
    Location
    Uk
    Posts
    8
    Rep Power
    0

    Re: Ecodan 14kw drawing 1.1A when off

    Quote Originally Posted by install monkey View Post
    Thank you, i've been looking through this but can't find a 'stand by' power consumption...so still unsure if i have fault or not.

  16. #16
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Ecodan 14kw drawing 1.1A when off

    from the drawing there is no crankcase heater, so the use of applying voltage to the windings is correct, is there an interface unit on it- as its powered off s1s2s3 is there any heater element in there as 1.1amp is high for powering electronics

  17. #17
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Ecodan 14kw drawing 1.1A when off


  18. #18
    Join Date
    Sep 2014
    Location
    Uk
    Posts
    8
    Rep Power
    0

    Re: Ecodan 14kw drawing 1.1A when off

    No, the interface unit is just electronics and has its own mains power supply, the signal to the interface unit is 24V dc. Could the transformer on the main board be the culprit?

  19. #19
    Join Date
    Sep 2014
    Location
    Uk
    Posts
    8
    Rep Power
    0

    Re: Ecodan 14kw drawing 1.1A when off

    Quote Originally Posted by install monkey View Post
    I don't have one of these installed, the interface unit is a flow temperature controller,

    http://www.celsiusair.co.uk/equipmen...-IF021B-E).pdf

  20. #20
    Join Date
    Sep 2014
    Location
    Uk
    Posts
    8
    Rep Power
    0

    Re: Ecodan 14kw drawing 1.1A when off

    Quote Originally Posted by Tayters View Post
    Hi Simon,

    Came across this (on a Fujitsu split a few years back. Measuring with an amp clamp gave a high reading like yours when unit was at rest but if you used a power meter or whatever they are called - one that takes into account the power factor then actual current was very low.

    I'm no expert in power factors but it's something like if the current and voltage are in phase then power factor is one and perfect for an amp clamp. If it isn't then your amp clamp gives a false reading. AC units have a part of the PCB to improve the power factor which is where all this grief stems from.

    You can pick the meters up from Maplins or RS fairly cheap (search energy meters) or get stuck in and buy a posh one but it might pay to check this first before looking for a fault which might not be there.

    Incidentally your electric meter at home takes the power factor into account so don't panic there. As for how does current lead or lag the voltage, well don't think I'll ever get my head around that one.

    Cheers,
    Andy.

    I thought i had convinced myself it was drawing current continuously, having tested it with current clamp & rms inline multimeter, finally tested it with a power meter, and shows 1.1A, 238V, but only 10W being consumed.

    Having spoken to an electrical guru, put bluntly, the capacitors will be charging/discharging with the ac phase so the 1.1 A i've been reading is being thrown back and forth from the unit. A resistive load draws current and P = V.I, but a capacitive load is more complicated and way over my head, but am happy my heat pump is ok.

    Thanks for your advice Andy that kept me questioning my readings and thank you to everyone else for your thoughts. All sorted.

    Cheers,

    Simon.

  21. #21
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Ecodan 14kw drawing 1.1A when off

    Thanks for the update, always good to know when technology has been beaten.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  22. #22
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,045
    Rep Power
    35

    Re: Ecodan 14kw drawing 1.1A when off

    Quote Originally Posted by Simon123 View Post
    I thought i had convinced myself it was drawing current continuously, having tested it with current clamp & rms inline multimeter, finally tested it with a power meter, and shows 1.1A, 238V, but only 10W being consumed.

    Having spoken to an electrical guru, put bluntly, the capacitors will be charging/discharging with the ac phase so the 1.1 A i've been reading is being thrown back and forth from the unit. A resistive load draws current and P = V.I, but a capacitive load is more complicated and way over my head, but am happy my heat pump is ok.

    Thanks for your advice Andy that kept me questioning my readings and thank you to everyone else for your thoughts. All sorted.

    Cheers,

    Simon.
    Top man, glad you got it sorted. Rumour has it if the receiver lands in the neighbours garden when it explodes Mitsi give you a prize.
    Health and safety first..........unless I'm in a hurry.