    When is 407C not 407C, fractionation



    Hi All,

    First post here.

    When is 407C not 407C, fractionation.

    We have just done a refrigerant analysis on a 407c system that had a leak in the aircooled condenser. We lost maybe 40% of the charge. Total charge 60lb.

    407C make up is: HFC-32 (23%), HFC-125 (25%), HFC-134a (52%).
    Test results today are:HFC-32 (27%), HFC-125 (28%), HFC-134a (45%).
    This shows a 7% loss of 134a.

    AHRAE states a tolerance of +-2%? I think.

    Does this test conclusion constitute a full system re-charge?

    Cheers, Rob W



  2. #2
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: When is 407C not 407C, fractionation

    Hi Robert
    The short answer is yes. Any of the new blends that have a high temp glide (more then 1 or 2) will fractionate and cause problems if the leak is on the gas side, this is the reason for liquid charging only.
    One of the results of your above situation will probably be high discharge pressures.
    Regards
    Paul
    Born to fish, forced to work

  3. #3
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: When is 407C not 407C, fractionation

    Thats very interesting seen as the other gases have gone up in percentage of the mix it appears mainly the 134a was lost. Im sure there is some type of equation can be done to show exactly what percentage of each gas was lost and what needs to go back in

  4. #4
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: When is 407C not 407C, fractionation

    Still the best and simplest answer is to find and repair the leak and then start again with new refrigerant charged in the liquid phase.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: When is 407C not 407C, fractionation

    .

    R134a tends to have the smallest atoms or molecules that make up the
    whole refrigerant, that is why R134a mostly is lost first and that is
    why you lose a higher % share of it in total.

    The only people who can re-blend this is the refrigerant manufacturer,
    the chance of you adding a bit of this and a bit of that to a fractured
    blend and then getting it to the correct blend would be almost impossible.

    You have a choice then! Do you remove it all and replace it with virgin
    refrigerant or do you run the risk of adding refrigerant to the blend in the
    hope it will be OK.

    Chances are you might get away with it but if it is still blended wrong
    afterwards then you will still have to remove it all and replace it.

    I always tell anyone who asks to replace the whole lot if the total charge
    is less than 10Kg. Below 10Kg it is not worth the hassle and the risk.

    If the system is above 10Kg you, your company and the customer have
    to make a commercial decision as to whether it is worth the risk of a
    fractured refrigerant weighed against the cost of a complete regas.

    Your decision and no easy answer because you just don't know what
    state your refrigerant is before you start and what if the system had
    leaked previously and already has had extra refrigerant added.

    What on earth would be in the system is anyone's guess, unless you go
    to the expense of having it analysed.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  6. #6
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: When is 407C not 407C, fractionation

    http://docs.lib.purdue.edu/cgi/viewc...&context=iracc

    all you need to show the client is in here..

  7. #7
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: When is 407C not 407C, fractionation

    Quote Originally Posted by r.bartlett View Post
    http://docs.lib.purdue.edu/cgi/viewc...&context=iracc

    all you need to show the client is in here..
    Interesting document.

    It shows what I thought would happen over successive leaks.
    No system is perfect but some are more prone to leaks than others
    and if you come to a fridge with 407 in it how many times before
    has it been repaired?

    If the paperwork and logs are all in place you could tell what had
    happened over the last year or so but every time you add to 407
    you dilute the mix to a point where it becomes useless to use.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..